Where do you start to criticize something like this (and mind you, I'm not an electrician): - What is the reason for all the holes punched in the ceiling? Clumsy footwork, bad initial placement of the ceiling cans, etc.? - What's wrong with having two switches that are so close together mounted on a two-gang plaster ring, rather than separate boxes (and, as it appears, not even at the same height)? - The sloppy, unsecured home runs to the breaker panel, and even the wiring inside it, have all the appearance of a poor temporary job at best. We have seen on this forum how neatly this work CAN be done by someone who cares about his workmanship. I see numerous white wires connected to breakers without being re-identified, and the panel itself seems awfully full for a new home, with very little room left for future additions. While this is a small thing, the installation of the service receptacle without using a close nipple or an offset really looks cheap. - I don't know much about the service entrance cable from the meter to the panel inside, but using conduit in this space seems a much better choice, and probably a lot safer. Is the main breaker in the panel, in fact, the only main disconnect, or is there one next to the meter outside? - I don't have a table for figuring wire fill, but it's even obvious to me that this box is way over the limit. Seeing six wirenuts in this box, including one on a single white wire, makes me think that the ex-EC even did a poor job of laying out this circuit.
Mike (mamills)
|
|
|
|
|
Joined: Nov 2002
Posts: 793 Likes: 3
Member
|
Too many breakers in that panel, yes? I think I see 43 breakers, and if I recall correctly the code's limit is 42.
|
|
|
|
|
Joined: Nov 2005
Posts: 507
Member
|
best thing that guy did was go out of business
|
|
|
|
|
Joined: May 2005
Posts: 247
Member
|
I count 44 breakers. (25 on the left, including 5 twins, 19 on the right including 2 twins.)
It looks like all the white wires connected to breakers are neutrals going to GFI or AFCI devices, and their associated pigtails, with the exception of 10/2 going to the dual 30 at the bottom right.
[This message has been edited by techie (edited 05-04-2006).]
|
|
|
|
|
Joined: Nov 2005
Posts: 187
Member
|
Picture #1 - He roughed for recessed lights and then he couldn't find the the wires. Why not put the housings in , in the rough?
Picture #2 - Why not a 2-gang? the switch on the right had wires in the box, but none to the switch?
Picture #3,4,5 - The builder finished the basement, he told the builder that he had to move the panel forward?
Picture #6 - 200-amp cable twisted, connectors on the meter socket were not even tightened.
Picture #7 - I count 13 conductors plus the grounds.
The basement two 3-ways and two 4-ways that did not work. He ran all of the travelers to one junction box, I counted eight 3-wires and two 2 wires in one standard 1900 box with no cover, I guess he couldn't get it on.
Hank
|
|
|
|
|
Joined: Mar 2006
Posts: 6
Junior Member
|
does the code reference 110.12 come to anyone else's mind?
Kurtis
|
|
|
|
|
Joined: Aug 2004
Posts: 54
Member
|
check out the "finished" carpentry....can you say "wood filler"!
|
|
|
|
|
Joined: Oct 2000
Posts: 4,165 Likes: 6
Member
|
Re: #2 It would be nice if the two switches matched.
Bill
Bill
|
|
|
|
|
Joined: Mar 2005
Posts: 169
Member
|
Saw too many breakers in the panel first off. Panel is a mess and the rest of the work is shoddy at best. As I usually say yuck what a mess!!
|
|
|
Posts: 201
Joined: April 2004
|
|
|
|