The "Twin & Earth" cable looks closer to UF cable IMO.
|
|
|
|
|
Joined: Mar 2004
Posts: 251
Member
|
T & E cable would make good switch legs here in the US, no re-identifing the white. LOL
|
|
|
|
|
Joined: Nov 2002
Posts: 793 Likes: 3
Member
|
Could you legally use the British "romex" in the USA? If it's listed or approved by the revalent British agnecy, is that good enough, or does the NEC require that the agency be an American outfit?
|
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I'd love to have some of that wire for DC circuits and switch loops! I have a feeling that the reduced GEC would be an issue. Is it available with a full-sized earth? Yes, it looks like UF. Are all y'all (that's plural for "y'all") aware that the Klein NM strippers also work very well on UF? These guys: http://www.kleintools.com/cutterstrippers/index.html
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
|
Joined: Dec 2005
Posts: 141
Member
|
I'm amazed that they both have solid earths. I don't think we have ever used solid earths in Australia. Stranded is much less likely to snap off at terminations. Stranded conductors are pretty much the norm here for everything except domestic light circuits. Much easier to work with and less likely to break. If you use single insulated wires in conduit runs are they solid too? That's when you really notice how much easier stranded is to use.
[This message has been edited by briselec (edited 04-15-2006).]
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
We use solid up to 10 AWG (40 amp capacity if that helps on the size)
All our NM 10 AWG and smaller is solid.
Snapping is not a problem and I like to work with solid.
Cables 'push' a lot farther when solid than when stranded.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
The T&E's conductors appears to be slightly smaller in diameter than the #12s. But still larger than #14. Like a #13
Is the ampacity between 15-20 Amps?
|
|
|
|
|
Joined: Dec 2005
Posts: 141
Member
|
Cables 'push' a lot farther when solid than when stranded Yes but pulling is a lot easier with stranded.
|
|
|
|
|
Joined: Apr 2005
Posts: 48
Member
|
What I'd like to know from you guys over the pond is why do you have all that "paper" stuffed into your cables? I have seen it many times and wondered.
In answer to the ampacity of 2.5mm T&E, it is rated at around 20Amps. The actual current depends on the conditions it is installed under e.g. in thermal insulation or in free air.
|
|
|
Posts: 440