(submitted via Joe Tedesco) I took this picture from a 1940 building, its a picture of disconnect switch mounted in the ceiling...
Eng. Sid Elahmad Electrical Engineer [This message has been edited by Webmaster (edited 06-14-2005).]
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
The disconnect is not much of a concern, check out the THHN(?) zip-tied out of the conduit from the left!!
I guess the disco violates the idea of readily accessable.
Stupid should be painful.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The height looks like a 'bit' over 6' 7", a violation of 404.8(A)
As for it facing down I do not believe that in itself is a violation.
Gotta wonder what is going on, that is a lot of disconnect connected to 1/2".
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Is it adjacent to the equipment it supplies? 240.24(A)(4), 404.8(A), exception 2.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
mxslick: oh and also the fact that the wires are entering that pipe without any protection from sharp edges?
|
|
|
|
Joined: Nov 2002
Posts: 174
Member
|
Missing KO on the disconnect. Is that a 4/0 cover on a 3/0 box? Appears to be a screw missing there.
|
|
|
|
Joined: May 2005
Posts: 247
Member
|
The wiring coming out of the conduit looks like coax and low voltage cabling.. possibly telephone or network, or CCTV. the sharp edge is still a concern, but not as much so..
|
|
|