Doesn't look too bad with the cover on - save for the "temporary" power strip screwed to the wall. Since the insulation is stripped back so far on the breakers, you get a good look at the conductors. The lower wire on the top twin 20 sure looks like it could be aluminum. In a word - UGLY
|
|
|
|
Joined: Jan 2005
Posts: 109
Member
|
Whats with the white wire on the twin breaker in the 2nd pic? 240v to the breaker under it? Do they make a handle tie for this 8^) Rod
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
It looks like a GFCI breaker with no load conductors to me.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
Isn't the GFCI wired with the LINE conductors coming into the LOAD terminals?
That might be a problem...
|
|
|
|
Joined: Jan 2005
Posts: 22
Member
|
is that 200A panel used as a sub panel? what i mean is, is the 2 aluminum fused some were else in line.
|
|
|
|
Joined: Aug 2003
Posts: 99
Member
|
the meter is on the other side of the wall, the 200 amp breaker was the first disconnect
|
|
|