Good Morning Don we can certainly agree to disagree.
I don't like how that looks anyway.
I do have a question.
I think the conduit runs are more than "short sections" to provide cable protection.
Where are we told they have to be short sections?
IMO 300.12 would be complied with if fittings where installed on the ends of the raceway as boxes are not required per 300.15(C) regardless of length.
If we do not need boxes just what is a complete raceway system?
10' of raceway with a fitting on both ends and two supports would be a complete raceway system in this case.
I am guessing the ambiguity here comes from the fact Chapter 3 was not really written with Article 800 in mind.
Good talking with you.
Bob