Wild Leg #11941
07/27/02 10:14 AM
07/27/02 10:14 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
In a 3 Phase service I have seen 240v between phases and a 208 to ground wild leg, What are some other combinations and where do they use the wild leg?


The Golden Rule - "The man with the gold makes the rule"
Work Gear for Electricians and the Trades
Re: Wild Leg #11942
07/27/02 11:26 AM
07/27/02 11:26 AM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Search for high leg (27 hits) or 4-wire delta (4 hits) at this site.

Note that “Bø” {or sometimes Cø} can also be called Stinger / Red / Orange / Purple / Power / Wild / Bastard / High Leg

Read through Scott35’s 3 Phase Delta Transformer Schematics in Technical Reference Area of this board.

Also see: home.att.net/~benmiller/elecsys.htm

Utility availability of this service type is usually limited to small, remote overhead systems.

Other non-symmetrical 3ø configurations are the corner-grounded variety.




[This message has been edited by Bjarney (edited 07-27-2002).]

Re: Wild Leg #11943
08/02/02 10:26 AM
08/02/02 10:26 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
I was unable to find any data in the technical Reference area.


The Golden Rule - "The man with the gold makes the rule"
Re: Wild Leg #11944
08/02/02 11:38 AM
08/02/02 11:38 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Al,

Did you set the selection to see all topics?
We are working on a way to have them continuously visible regardless of date, but this works for now. Look at the thread in that area for Instructions if you're not sure what I mean.

Bill

Re: Wild Leg #11945
08/02/02 06:08 PM
08/02/02 06:08 PM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Yep, I tried that, no subjects come up.


The Golden Rule - "The man with the gold makes the rule"
Re: Wild Leg #11946
08/02/02 06:22 PM
08/02/02 06:22 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Alda,
The wild leg is ONLY useful in configurations that do not require a neutral, such as 3 phase equipment, or 240 volt loads with no neutral, otherwise you burn it up.

You ONLY have a high leg in Delta systems (open or closed) because you tap mid phase of one coil (between A and C)

That's why the Wye is the popular form today, it creates no high leg and all 3 phases are useful with the neutral.

You often see 199 volt high legs, this is from 230 volt systems. Phase to ground voltage of A or C phase X 1.732 = phase to B voltage.

Re: Wild Leg #11947
08/02/02 06:57 PM
08/02/02 06:57 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Al,

Take a look to see if this is what you are looking for.
https://www.electrical-contractor.net/ubb/Forum15/HTML/000054.html

Bill

Re: Wild Leg #11948
08/02/02 07:49 PM
08/02/02 07:49 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
'Wild leg' is no longer the term i like.

Has you ever yelled out

got the WILD LEG'

in a crowded store or mall???

[This message has been edited by sparky (edited 08-02-2002).]

Re: Wild Leg #11949
08/04/02 02:22 AM
08/04/02 02:22 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Thanks for the answers, Bill great transformer drawings, but still not sure where they are used. On a 3ph system 240v between phases and measuring "120v to grd, 120v to gnd, and 208 to gnd", where would the 208v to gnd be used?


The Golden Rule - "The man with the gold makes the rule"
Re: Wild Leg #11950
08/04/02 07:20 AM
08/04/02 07:20 AM
E
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
Aldav53,

The high leg (208 to ground) exists as a result of the center tap, but is not used to supply loads.

Ed

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,198 Are you busy
189,177 Re: Forum
178,858 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 1.0237 MB (Peak: 1.1998 MB) Zlib enabled. Server Time: 2018-12-14 07:45:23 UTC