#115229 09/11/03 02:30 PM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
Paul, ThinkGood,
Yes, we are required to have an isolator for all socket-outlets, either as a part of the fitting itself or fitted adjacent to the equipment that it supplies.
wa2ise,
The switch is for turning the appliance off beforeyou unplug the thing, if you want to just pull the plug, that's fine, but, the plug contacts won't like it too much!. [Linked Image]

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

#115230 09/11/03 03:42 PM
Joined: Aug 2002
Posts: 1,081
T
Member
Ya learn somethin' new every day!

Thanks.

#115231 09/11/03 03:54 PM
Joined: Nov 2001
Posts: 745
M
Member
Pauluk/Trumpy:
Is this interrupting device simply a switch, with an actual OCPD located elsewhere, i.e. at the main service panel?

Also, aren't there some types of male connectors made that incorporate a small fuse?

Mike (mamills)

#115232 09/11/03 04:32 PM
Joined: Aug 2001
Posts: 7,520
P
Member
On the British receptacles, it's purely a switch (used to be single-pole only, but some makes now have double-pole switching). The OCPD is at the main panel, and may be up to 32A depending upon the circuit arrangement.

The BS1363 plugs which fit the outlet pictured above will all carry a fuse. It's part of the original specification for this type of connector:
[Linked Image]

I'm not sure if there are any Aussie/NZ plugs with fuses, but then they don't use 30A ring circuits!


[This message has been edited by pauluk (edited 09-11-2003).]

#115233 09/12/03 05:44 PM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
Paul,
No, we don't have fuses in our plugs, although we probably should, would save us Faultsmen a few late night callouts.
We do have ring-circuits here, but they are limited to use in caravan parks.
BTW,Paul, I can't really remember the last time that I actually used a double pole switch, as this sort of thing is really only used on 2 phase 230/400V stuff and even this is getting pretty rare these days. [Linked Image]
Mike,
The switch that is used in our socket-outlets is just a single-pole device and has no OCPD function, although you can get socket-outlets with an integral RCD (GFCI) unit in them.

[Edited to correct a few spelling mistakes,
words seem to be coming out backwards, this morning!. [Linked Image]]

[This message has been edited by Trumpy (edited 09-12-2003).]

#115234 09/14/03 07:54 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Quote
although you can get socket-outlets with an integral RCD (GFCI) unit in them.
The same applies in Britain, although these devices tend to be very expensive and not widely used:

[Linked Image from tlc-direct.co.uk]
This one is listed at around $37 each.


[This message has been edited by pauluk (edited 09-14-2003).]