ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
2 members (Scott35, ampherder), 263 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
[Linked Image]
Quote
Yup, it's the world's cheapest T-Switch here, but would you use it?

~Steve aka sparky

[This message has been edited by Webmaster (edited 08-12-2003).]

Joined: Aug 2002
Posts: 1,081
T
Member
Quote
...would you use it?

Do you mean with or without PPE?

Joined: Dec 2002
Posts: 228
J
Member
I was not aware that you could clamp sealtight with a NM connector, and I have been buying the expensive ones all along.... BTW what are the two wires exiting the panel on the bottom left, ground wire?

Joined: Nov 2001
Posts: 745
M
Member
I have seen these SqD devices and played with them. FWIW, I'm kinda surprised at SqD for offering such a product for isolating generator current from POCO current - it just seems kinda cheesy to me. [Linked Image] My personal choice would be a double-throw, center-off safety switch (along with properly fitted connectors to the box, of course).

Mike (mamills)

[This message has been edited by mamills (edited 08-12-2003).]

Joined: Oct 2000
Posts: 5,392
S
Member
This isn't my work fellas,
but that $.02 T-switch would most certianly beat my quotes.

Joined: Apr 2002
Posts: 2,527
B
Moderator
This type of pictured circuit-beaker “intelock” is sometimes found in RVs to select between an on-board genset and “shore power.” I am not sure many electric utilities have caught on to this potential death trap. What amazes me is the 2-pole breaker across from a 1-pole breaker—backfeed guaranteed, unless only one pole of the 2-pole breaker is used. On its best day that can’t work without significant hazard to life and property—unless this is a 100% “off-grid” system.

[Linked Image from 64.146.180.232]

{The white left enclosure looks like a Trace inverter accessory—the installation may be for a photovoltaic home-power installation.}

Joined: Jan 2003
Posts: 4,391
I
Moderator
OK how do you guys feel about this one, (maybe someone can enlarge it)

[Linked Image from reliancecontrols.com]

Reliance Controls

I was thinking about using this in my own house, the mechanism is not flimsy but it removes with the cover.

For the average DIYer this could be a problem.

Bob

[This message has been edited by iwire (edited 08-12-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Bob,

Here's a 2x version, anything past that gets really distorted.

[Linked Image]

I REALLY don't like the idea of it coming off with the cover.

Bill


Bill
Joined: Oct 2000
Posts: 5,392
S
Member
i concere with the group here, but lack the verbage to convey the sentiment other than 'cheesy'

Bjarney (et all) could you please elaborate??

Joined: Nov 2001
Posts: 745
M
Member
Sparky:
I guess the thing I don't like about it is that the little "either/or" arm (for lack of a better description) looks very flimsy - as a matter of fact, when I was "playing" with one (not installed) I found it rather easy to bend the arm out, allowing both breakers to be closed (not good [Linked Image] ). I hope the one I was handling was the exception and not the rule.

Mike (mamills)

[This message has been edited by mamills (edited 08-12-2003).]