Member
May be it's just that it's Monday, but I'm still a little confused.

What is your primary system - 480 delta or 480Y/277?


You say you are measuring a voltage from the "neutral to the equipment ground conductor". By this do you mean from the control transformer "neutral" to the control panel ground? Or do you mean from the control panel neutral to the building ground?

As, I said, my head is a little fuzzy this morning so I don't know if this is going to be valuable. Could I get a couple of more voltage readings? (Grid is your 480 system, CPT is from your control transformer)
480 grid phase A to grid neutral
480 grid phase B to grid neutral
480 grid phase C to grid neutral
480 grid phase A to grid ground
480 grid phase B to grid ground
480 grid phase C to grid ground
480 grid phase A to panel ground
480 grid phase B to panel ground
480 grid phase C to panel ground
480 grid neutral to grid ground
120 panel hot to grid neutral
120 panel hot to grid ground
120 panel neutral to grid ground
120 panel neutral to panel ground

Also what happens when you lift the ground connection from the control transformer.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#11408 07/16/02 07:15 PM
Joined: Oct 2001
Posts: 41
R
rkukl Offline OP
Member
Hi all
Here’s what we finally found almost seems anti-climatic. It seems that the hot and neutral were reversed at the faceless GFCI. Should have known better and checked that in the beginning. Oh well at least we found the problem and all is well.
Thanks for all your replies
Rich

#11409 07/16/02 07:58 PM
Joined: Oct 2000
Posts: 5,393
S
Member
mama said there'd be days like this....

thanks for the update Rich....

Page 2 of 2 1 2