Forwarded by Joe Tedesco:

[Linked Image]

[Linked Image]
Quote
Here is a picture of my outside 200 amp service panel and inside sub panel. There were no violations on this inspection.

Jerry Gilley

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
I hate to be nit-picky, but the GRC nipple could be argued to be a violation of 250.6(A) and it appears that 250.92(B) may be violated if the KO's have any eccentric or concentric rings left on the box where the nipple is connected (and assuming there is no bonding bushing in the meterbase that I wouldn't be able to see).

PVC will solve both problems in the future.

That's one that I learned raht-cheer on ECN!

(Thanks Bill)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Actually, I lied...

I LOVE to be nit-picky!!!

[Linked Image]

Not a violation, but, no 40 space MLO's?

[This message has been edited by sparky66wv (edited 09-15-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Oct 2000
Posts: 4,161
Likes: 5
Member
What do you think about the 200A sub (w/main) being fed from a 100A breaker?

Bill


Bill
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
I suppose as long as the lugs on the Main Breaker and the Neutral and EGC Lugs are rated for the size of wire used, it still offers a convenient "bus disconnect" and the 22KAIC protection.

Plus, like here, a 200A 30 or 40 space MLO may be actually more expensive and require a special order!

Not a code violation, but my PoCo requirements would want the straps on the mast within 12" of the meterbase (minimum 30" spacing and within 12" of the weather head).

[This message has been edited by sparky66wv (edited 09-16-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Apr 2002
Posts: 558
C
Member
Why are there white wires connected to the circuit breakers without re-identification? The breaker in the upper left corner of the main panel looks like a Siemens not GE. Most of the cables in the main panel appear to enter through 1 KO and I have never seen a connector listed for more the 4 cables. The main lugs on 200 amp GE load centers are listed for min. #1 conductors and the wires feeding the sub panel look smaller but its hard to tell with this picture.


Curt Swartz
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Wow, I missed all that at first...

I've got to go to bed...

(Note time of post)

Oh, to add... Just a hunch, but the service entrance neutral connected to the top lug of the meterbase and the service feeder neutral appears to have been stripped from a piece of SER (going by the white stripe). I would think that THWN or RHW-2 or the like would be required here.

[This message has been edited by sparky66wv (edited 09-16-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Mar 2001
Posts: 2,056
R
Member
Is that rigid nipple OK between the meter socket & panel? Should it be a Meyers hub?
The GEC connection is made at the meter socket. I believe our PoCo forbids that.
Also, although not a violation, see my post about excessive NM jacket in the panel.

Joined: May 2001
Posts: 552
T
Member
Is there a connector on the egc at the meter or is it routed through 1/4 inch k.o? [Linked Image]


Donnie
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
LOL at txsparky.... You're a bad man!

[Linked Image]

Redsy, yep, that's what I was getting at with the GRC Nipple violating 250.6(A)for parallel current paths and perhaps 250.92(B)for a lack of bonding bushing.

I still can't believe I didn't see all those white conductors before!

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI