Submitted by Virgil Kelly (aka '66)"Complete with "duct tape" bushing"
|
|
|
|
Anonymous
Unregistered
|
Hey, if the bricks are fake...
Duct tape is gray, but spray it with some "Zinc-It" to make it look like the real thing for sure.
|
|
|
|
Joined: Oct 2000
Posts: 4,143 Likes: 4
Member
|
'66,
I would think that the meter readers would be trained to spot and report hazards like this to the Utility. Got any idea how long it's been like this or how it came to be like this?
Just curious, around here the owner probably would have gotten a letter threatening disconnection if the violation wasn't resolved.
Bill
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
I can tell you exactly how long it's been there... Since August of 1975. The retired mining electrician neighbor of mine did this.
Hint: I took this picture on Mother's Day.
The CB has been replaced once and needs replaced again. It's even SQ D, so it ain't GE's fault here... I've already replaced the FPE panel inside. The requisite SO cable is feeding the well pump, very dry rotted too. I'd like to eliminate the pole, mast mount the MB back to back with the panel and eliminate the disco too.
[This message has been edited by sparky66wv (edited 05-15-2001).]
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
I've been told by employees of Alegheny Power (the serving utility for Virgil & me) that once a service is hooked up, non-payment is the surest way to get it turned off. AP will leave stuff like this in service for years, especially since the biggest problems come after the meter. You should have heard their linemen complaining about us inspectors when we first started in WV. They usually opened with "I know what's safe."
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
While we're on the subject, why do mobile homes attract tornadoes & so much inferior electrical work?
There are four installations like this one in a mobile home park near here (I'm refering to the conductors without conduit).
In the other mobile home park in this town, I'd be afraid to stick a shovel in the ground, many of the feeders are buried 6" or less.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Oct 2000
Posts: 4,143 Likes: 4
Member
|
I don't want to make a long story out of it, but here's my experience with Mobile Homes.
Got a call after Midnite Dec 23rd anout 10 yrs ago. Trailer park near here, (really only about 8 - 10 trailers) Utility had turned off their electrical service and gas (propane) and they had no heat. After making sure the gas was off I reset the meter to run some tests. What I found was a Long, Long list of problems. Here are some of the most memorable:
Panelboard was on the floor (loose) under a bed facing up no cover. No bonding to the Frame. Supply cord (they plugged into receptacles) was frayed and reverse polarity. Christmas lights were screwed on to the outside metal siding between the wires. There was a gas leak from the propane tank in front (I was told). The trailer skin had 29 volts on it and was arcing to the gas line where it went through the skirt.
These people really saw nothing wrong with any of this (the old 'it's been like that' thing) and thought the Fire Marshall (whom they called at 2:00 am) was being unreasonable in having them shut down.
Bill
Bill
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
An old horse trader I know had the neutral connection come apart on the "feeder" (14-2 with the ground cut off) to one of his house trailer/tack rooms. It knocked him on his tail when he stepped out barefoot to see why his lights went out. I shut off the power, and offered to fix it for free. He said he didn't want to fix it right,it didn't bother him to have the trailer hot,& he'd be careful, but he wanted some lights. He bought 500' of rotted cord at the auction, and ran 2 wire extension cords all over to clamp lights. He was happy. What a stubborn old curmudgeon.
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
It's amazing in that these things are so obvious to the trade, and not the public! boy, they sure are out there !!!
|
|
|
|
Joined: Apr 2004
Posts: 812
Member
|
I don't feel safe where I live anymore. The trailer that was just installed down the road from me has some errors, some serious, some not-so-serious, and some critical! #1. 10AWG wire used for a 50AMP Air conditioner. #2. Electrical conduit on ground in crawlspace (local code) #3. No GFCI in crawlspace for pipe warmer #4. UF used for AC feeder in crawlspace (No conduit, local code) #5. Electrical ground bonded to copper GAS line! At my house and in/under many others: #1. Romex/NM on ground #2. No conduit in crawlspace #3. No grounding rod, only to water line #4. Rubber insulated feeder cable w/ plug from meter, goes underground, slithers in crawlspace.
[This message has been edited by Theelectrikid (edited 04-09-2005).]