Submitted by S. Wilson (electure)


The tenants in this bldg. mentioned that they were pleased to see that someone installed barricades to protect their forklift chargers. (There was another one right up against that tranny, but they moved it so I could get to the trans... & verify that it was cooked!)

S.Wilson

Horizontal Ad
#112185 04/22/01 11:02 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Ahh, one of my favorite violations.

Working clearance? We don't need no stinking working clearance.

Besides working clearance (mainly for the panel & safety switch), was there adequate ventilation clearance for the transformer? Most of the ones I've dealt with required 6" of clearance on the backside.

Tom

[This message has been edited by Tom (edited 04-22-2001).]


Few things are harder to put up with than the annoyance of a good example.
#112186 04/22/01 01:17 PM
Joined: Oct 2000
Posts: 4,145
Likes: 4
Member
Tom,

You're reading my mind!
That transformer looks like it's right up against the wall.


electrure,

What was the reason for failure? Any ideas?

Bill


Bill
#112187 04/23/01 07:13 AM
Joined: Dec 2000
Posts: 4,294
Member
The trans was blocked on 3 sides (that's a sheet of plywood) but did have 6" in back.
The old one was scrapped before I had a chance to check it out. The 90 A primary C/B was tripped. When I tried to reset it, it took out the GFI for the building. When replaced, the secondary load was less than 100A It's a 75 KVA with 200A Main in Load Center. Any ideas??? (that's smoke on the wall)

[This message has been edited by electure (edited 04-23-2001).]

#112188 04/25/01 05:27 AM
Joined: Oct 2000
Posts: 5,393
S
Member
electure;
fried primary, dead short ? better a main GFI that the entire punch going to the prim CB !

[Linked Image]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,294
Joined: December 2000
Top Posters(30 Days)
Popular Topics(Views)
333,575 Are you busy
258,949 Re: Forum
240,376 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5