0 members (),
506
guests, and
19
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
While there might be some debate as to using SO for a water heater, I think we can all agree that using a light-duty extension cord to power the emergency lights is, well, a little too resourceful!
- renosteinke
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
SO for a water heater a violation in my opinion of 400.8(1) 400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1)As a substitute for the fixed wiring of a structure Cord and Plug connected EBUs allowed within limits. Part of 700.12(F) Flexible cord-and-plug connection shall be permitted, provided that the cord does not exceed 900 mm (3 ft) in length. The cord looks longer than 3'
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
No Code book this morn, but to add to Bob's post, the emergency unit can't be cord connected if it is a REQUIRED emergency light for means of egress. If it's just for your convenience, you can connect them with 3' cords until the cows come home.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Bob and Scott, Coming from a place like I do, we are required to wire any sort of Emergency lighting into a permanent supply. That means hard wired, with no cords. The wires would enter through the back of the fitting. It also prevents someone from in advertantly disconnecting your Em lighting system.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Oh and by the way guys, is it a requirement to have a disconnect "within sight" while working on that Cylinder?. Over here you must have an adjacent isolator at the Hot water cylinder. BTW, that cord used on that cylinder looks far too DIY for my liking.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
the emergency unit can't be cord connected if it is a REQUIRED emergency light for means of egress. Not that I have ever cord and plug connected an emergency light but it is allowed by the NEC to do that with even required emergency lights. The article I quoted is 700 which covers the required emergency lighting. That aside I would have no trouble believing another code prohibits it. It seems like a poor practice. Here in MA they have deleted the sentence from 700.12(F) that allows cord and plug connection. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2005
Posts: 141
Member
|
At least the SO isn't embedded in drywall mud like it was in my house. BTW I found a whole bunch more of that wiring "method" behind a couple of more fixtures in the basement.
I'm now in the process of removing ALL the new drywall that these twits put up so I can rewire the whole basement.
|
|
|
Posts: 7,382
Joined: April 2002
|
|
|
|
|