#10977 06/25/02 04:10 PM
Joined: Jan 2002
Posts: 34
M
menegt Offline OP
Member
A colleague of mine posed this question to me today. He is doing a side job for a friend. He has to hook-up a 40A 240V single phase spa. He is running (2)#6's but found out that he had to up the neutral size to #4 (per manufacture - owners manual). Not sure why he had to. Is there any reason to have the neutral larger than the other ungrounded conductors? I told him I have not run across any situation where the neutral had to larger in any circumstance. He told me he ran a "high" harmonics xfmr which needed a larger neutral? Any responses appreciated.

#10978 06/25/02 08:58 PM
Joined: Apr 2002
Posts: 914
E
Member
I've seen a few circumstances that require a larger neutral, but I can't see why for a hot tub, if you find out let us know.

#10979 06/25/02 11:26 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
I'll bet it's because the spa manufacturer can demand it in the instructions and that won't preclude getting UL labeling. It's no skin off their backs.

#10980 06/26/02 06:32 AM
Joined: Oct 2000
Posts: 5,392
S
Member
most of the load is the heater, the motors are small....there's really no harmonica in the tub.....

#10981 06/26/02 02:16 PM
Joined: Nov 2001
Posts: 280
M
Member
My question is why the need to oversize the neutral, 240 volt residential, the neutral will the 'difference ' of the two legs, ie 20 on A and 25 on B then the total on the nutral will be 5 amps.
The heaters are generally 240 volts on both and the neutral is not involved, balance.
What am I missing here, it doesnt make sense to oversize the neutral in this case.
Right ???!!

-Mark-

#10982 06/26/02 08:26 PM
Joined: Jan 2002
Posts: 34
M
menegt Offline OP
Member
The high harmonics xfmr was just another instance where he had to up the neutral. The hot tub is another situation. ( i don't see the reason to up the neutral (secondary) in the xfmr situation either!!

#10983 06/26/02 08:39 PM
Joined: Oct 2000
Posts: 5,392
S
Member
are U sure it wasn't the G-wire to said tub?

#10984 06/27/02 12:28 AM
Joined: Jan 2002
Posts: 34
M
menegt Offline OP
Member
I don't think it was the ground that would've been oversized. Also if i recall somewhere in the codebook that the equipment ground was never supposed to be larger than the grounded conductor.

#10985 06/27/02 11:05 PM
Joined: May 2002
Posts: 68
H
Member
menegt Some of these hot tubs have two heating elements that use the neutral and if one of them opens then all of the load is thrown on the neutral most of these self contained hot tubs are set up to be connected to 110v by changing the hookup cord and not useing both heating elements and the motors also are 110v


Be Fair, Be Safe
Just don't be Fairly Safe
#10986 06/29/02 01:00 AM
Joined: Oct 2000
Posts: 2,722
Broom Pusher and
Member
The term "High Harmonics Transformer", was this something that was quoted in the book?

Sounds like a mistake in printing or something.

Just curious... [Linked Image]

Scott S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
BigB 3
jt7 3
Popular Topics(Views)
305,255 Are you busy
233,609 Re: Forum
218,259 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5