Buried LB #109458
10/22/05 12:01 PM
10/22/05 12:01 PM
Admin  Offline
Joined: Oct 2000
Posts: 3,495
Went to install a dryer circuit and found this partially buried lb.

[Linked Image]

[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: Buried LB #109459
10/22/05 12:50 PM
10/22/05 12:50 PM
Lostazhell  Offline
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
Something about this smells like a back porch gone utility room via the local handyman.... Lack of strapping on anything south of the panel and the buried LB almost make me cringe at the thought of what might be hiding in the panel [Linked Image]


Re: Buried LB #109460
10/22/05 03:14 PM
10/22/05 03:14 PM
mamills  Offline
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
I've never been crazy about seeing a panel installed upside down because the service conductors enter from the bottom - or for any other reason.

Poor substitute for a proper workmanship-like job.

Mike (mamills)

Re: Buried LB #109461
10/23/05 12:53 AM
10/23/05 12:53 AM
Larry Fine  Offline
Joined: Feb 2005
Posts: 693
Richmond, VA
[Linked Image]

Larry Fine
Fine Electric Co.
Re: Buried LB #109462
10/23/05 01:35 AM
10/23/05 01:35 AM
caselec  Offline
Joined: Apr 2002
Posts: 558
San Jose, CA

Why do you say this panel is upside down? Most loadcenters are designed to be mounted either way. If the feed is coming from the bottom the lugs should be on the bottom.


Curt Swartz
Re: Buried LB #109463
10/30/05 04:33 PM
10/30/05 04:33 PM
electronspark  Offline
Junior Member
Joined: Sep 2005
Posts: 8
just curious, is it against code to have a lb buried like this? i mean after all it's not a junction box, if it were a solid piece of conduit to the meter it wouldn't be accessible anyways, i could however see of the service conductors were to be replaced it would be a major PITA- Thanks

[This message has been edited by electronspark (edited 10-30-2005).]

[This message has been edited by electronspark (edited 10-30-2005).]

Re: Buried LB #109464
11/04/05 09:58 PM
11/04/05 09:58 PM
yaktx  Offline
Joined: Feb 2003
Posts: 288
Austin, Texas, USA
"Why do you say this panel is upside down? Most loadcenters are designed to be mounted either way. If the feed is coming from the bottom the lugs should be on the bottom."

There was a code change some years back which outlawed any panelboard installation where the on/off wording on any breaker would appear upside down, or where the handle, when in the "on" position, would be pointing down. I forget when this took place. (Think 12-circuit Stab-Lok).

Since that time, manufacturers have reconfigured their equipment so that all breakers throw side-to-side. If no breakers are in an up-down orientation, there is nothing wrong with mounting them "upside down".

Of course, if it is a 3R enclosure, it will only go one way.


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,860 Are you busy
181,981 Re: Forum
172,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9848 MB (Peak: 1.1394 MB) Zlib enabled. Server Time: 2018-03-23 10:38:52 UTC