Repair Garages #109023 11/10/03 06:47 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
In a repair garage, the area up to 18" is considered a Class 1 Div 2 location.
These folks did put in the required conduit seals at about 20", but I think there's still a problem.
[Linked Image]
What do ya think?

2017 / 2014 NEC & Related Books and Study Guides
Re: Repair Garages #109024 11/10/03 06:59 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
Are those EMT connectors coming into the bottom of the sealoffs???

Re: Repair Garages #109025 11/10/03 07:30 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
Certainly are!
So, what's the problem?

Re: Repair Garages #109026 11/10/03 07:40 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
Well, EMT isn't allowed in a Class 1 Div 2 area per 501.4(B), assuming that this is power wiring not exempted under 501.4(B)3.

If the conduit is rigid or IMC, then the use of EMT connectors on it would be a violation of listing requirements under 110.3(B).

Re: Repair Garages #109027 11/11/03 07:08 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
You got it right on the money, but
This one's double-trouble!.
Although not shown, right up above is a panelboard.
That's a waterline to a drinking fountain.(Why would anyone run a 3/4" plumbing feed to a single drinking fountain?)...S

[This message has been edited by electure (edited 11-11-2003).]

Re: Repair Garages #109028 11/11/03 07:46 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Electure, did you check to see if the sealoffs were filled?

Roger

Re: Repair Garages #109029 11/11/03 08:39 PM
Joined: Aug 2002
Posts: 1,081
T
ThinkGood Offline
Member
Would somebody please "translate" this into layman's terms?

Re: Repair Garages #109030 11/11/03 08:58 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
Some areas in repair garages are considered "classified areas", primarily because of the potential for fuel vapor buildup. Wiring in such areas is subject to very demanding requirements, including the use of rigid or IMC conduit, threaded connections, explosionproof boxes and fixtures, and proper sealing to prevent flammable vapors from moving through the conduit to remote locations.

The fittings shown here are called "sealoffs" or "EY seals", and are used to physically seal the conduit at the boundary of the hazardous area. After the wires are pulled, a liquid sealing compound is poured into the fitting (through the plugs with the square recesses), which fills up the spaces around the wires and prevents flammable vapors from passing the seal.

The use of EMT fittings could allow flames and hot gases from a vapor explosion inside the conduit system to ignite the surrounding atmosphere. Only threaded connections are allowed here.

The requirements for wiring in hazardous locations are spelled out in Articles 500 and 501 of the NEC.

Re: Repair Garages #109031 11/12/03 12:27 AM
Joined: Jul 2003
Posts: 394
B
Big Jim Offline
Member
Maybe the water line will rupture and put out the fire after the explosion. a 3/4 line would really help then

Re: Repair Garages #109032 11/12/03 08:29 AM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
I pulled one of the plugs, and yes, these were poured. There was even a little dab of NoAlox, or some anti-sieze lube, on the threads of the plug!
The waterline run through the dedicated space for the panelboard is a violation as well.

TG, before the liquid is poured in, a fiber material is driven into the conduit to keep the liquid sealing compound (one mfr. calls their's "Chico") from pouring down the conduit.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,434
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,901 Are you busy
205,763 Re: Forum
193,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3