In a repair garage, the area up to 18" is considered a Class 1 Div 2 location.
These folks did put in the required conduit seals at about 20", but I think there's still a problem.
[Linked Image]
What do ya think?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#109024 11/10/03 07:59 PM
Joined: Sep 2001
Posts: 806
N
Member
Are those EMT connectors coming into the bottom of the sealoffs???

#109025 11/10/03 08:30 PM
Joined: Dec 2000
Posts: 4,291
Member
Certainly are!
So, what's the problem?

#109026 11/10/03 08:40 PM
Joined: Sep 2001
Posts: 806
N
Member
Well, EMT isn't allowed in a Class 1 Div 2 area per 501.4(B), assuming that this is power wiring not exempted under 501.4(B)3.

If the conduit is rigid or IMC, then the use of EMT connectors on it would be a violation of listing requirements under 110.3(B).

#109027 11/11/03 08:08 PM
Joined: Dec 2000
Posts: 4,291
Member
You got it right on the money, but
This one's double-trouble!.
Although not shown, right up above is a panelboard.
That's a waterline to a drinking fountain.(Why would anyone run a 3/4" plumbing feed to a single drinking fountain?)...S

[This message has been edited by electure (edited 11-11-2003).]

#109028 11/11/03 08:46 PM
Joined: May 2002
Posts: 1,716
R
Member
Electure, did you check to see if the sealoffs were filled?

Roger

#109029 11/11/03 09:39 PM
Joined: Aug 2002
Posts: 1,081
T
Member
Would somebody please "translate" this into layman's terms?

#109030 11/11/03 09:58 PM
Joined: Sep 2001
Posts: 806
N
Member
Some areas in repair garages are considered "classified areas", primarily because of the potential for fuel vapor buildup. Wiring in such areas is subject to very demanding requirements, including the use of rigid or IMC conduit, threaded connections, explosionproof boxes and fixtures, and proper sealing to prevent flammable vapors from moving through the conduit to remote locations.

The fittings shown here are called "sealoffs" or "EY seals", and are used to physically seal the conduit at the boundary of the hazardous area. After the wires are pulled, a liquid sealing compound is poured into the fitting (through the plugs with the square recesses), which fills up the spaces around the wires and prevents flammable vapors from passing the seal.

The use of EMT fittings could allow flames and hot gases from a vapor explosion inside the conduit system to ignite the surrounding atmosphere. Only threaded connections are allowed here.

The requirements for wiring in hazardous locations are spelled out in Articles 500 and 501 of the NEC.

#109031 11/12/03 01:27 AM
Joined: Jul 2003
Posts: 394
B
Member
Maybe the water line will rupture and put out the fire after the explosion. a 3/4 line would really help then

#109032 11/12/03 09:29 AM
Joined: Dec 2000
Posts: 4,291
Member
I pulled one of the plugs, and yes, these were poured. There was even a little dab of NoAlox, or some anti-sieze lube, on the threads of the plug!
The waterline run through the dedicated space for the panelboard is a violation as well.

TG, before the liquid is poured in, a fiber material is driven into the conduit to keep the liquid sealing compound (one mfr. calls their's "Chico") from pouring down the conduit.

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
triple 2
dsk 1
Popular Topics(Views)
304,924 Are you busy
233,346 Re: Forum
218,068 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5