harmonic noise? #10768 06/18/02 08:14 AM
Joined: Jun 2002
Posts: 2
M
Mustang Offline OP
Junior Member
We have a degater machine(240v 3 phase) that has a AB variable frequency drive. Anywhere we plug this machine up it sends a lot of noise all the way back to the panel and affects the other equipment coming off that panel, digital displays go nuts! what can I use to get rid of this?

Work Gear for Electricians and the Trades
Re: harmonic noise? #10769 06/18/02 11:38 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
What model Drive is it?
AB makes Line Reactors to help mitigate harmonics which are fed back into the power line from the Drive.
MTE corp. offers the same, and are quite a bit cheaper.
They are not expensive at all. I believe a 10 HP unit costs less than $150.00

[This message has been edited by Redsy (edited 06-18-2002).]

Re: harmonic noise? #10770 06/23/02 10:50 AM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
I would be asking questions of the ‘degater’ {what is that?} supplier, and maybe AB could help in that they are interested that their products are applied correctly. Sounds a little fishy though. Make sure to get a copy of AB’s drive installation instructions and see that it is installed exactly to their specs. Get ready for some finger pointing. Proceed carefully. If your job was to provide a powered receptacle for the degater, you can probably, by rights, walk away from it as you are done with your assignment.

But then, it could be a good experience finding out what the exact problem and cure is. Get straight exactly who pays for what early on. It’s extremely difficult to remotely troubleshoot an odd problem, but make notes on who said what if you take on the troubleshooting task. If possible, be there when the degater expert works on his machine. Be wary of things like oddball/non-code grounding [or ungrounding.] Their obligation is to provide a working piece of equipment that doesn’t interfere with other stuff that is/was OK before degater powerup.

Reputable equipment suppliers will usually pay you for your work in fixing their problem, but get that cleared up early on, because they might get flakey at some point. Do not change anything on the degater unless you have written instructions from ‘degater central,’ and that you understand exactly what they want you to do.

Study up on it Mustang, but generally there are 3% and 5% reactors. In your case it probably needs to be installed wired between the panelboard and drive. It may need to be configured so that control power on the degater is fed upstream of the reactor…you may have to experiment—no guarantees. In extreme cases a Ä-Y drive-isolation transformer may be required.


[This message has been edited by Bjarney (edited 06-23-2002).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
270,999 Are you busy
205,003 Re: Forum
193,121 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3