#107175 11/26/04 07:22 AM
Joined: Dec 2000
Posts: 4,295
Member
(Courtesy of Joe Tedesco)


[Linked Image]

[Linked Image]

[Linked Image]

Horizontal Ad
#107176 11/26/04 03:16 PM
Joined: Oct 2004
Posts: 806
Member
Gotta love the "ample" wire bending space in these panels. [Linked Image]

How did this junk ever get listed?

(Panel maker's name omitted to protect the guilty.)


Stupid should be painful.
#107177 11/26/04 05:56 PM
Joined: Aug 2002
Posts: 1,691
S
Member
Are those scorch marks I see on the bottom right-hand corner?

I'd love to know the brand of the panel, that way we know to avoid buying it!

#107178 11/26/04 09:05 PM
Joined: Dec 2000
Posts: 4,295
Member
Holey Panel & Holy Smoke [Linked Image]

#107179 11/26/04 10:50 PM
Joined: Sep 2002
Posts: 946
Likes: 2
N
Member
How did this stuff ever get listed? Look at Zinsco and then ask the same question.

#107180 11/26/04 11:00 PM
Joined: Nov 2001
Posts: 42
A
Member
looks like the cement slab below sunk causing the fittings to pull out of the enclosure , common on long island usually 2-3 years after the pour..


JBIELECTRIC EAST MEADOW NY
#107181 11/26/04 11:40 PM
Joined: Jan 2002
Posts: 36
N
Member
Looks like a GE All-In-One. Atleast thats what those slim "mini's" lead me to believe.
But the bottom 2 pole is a Cutler Hammer.

Horizontal Ad
#107182 11/27/04 01:22 AM
Joined: Sep 2002
Posts: 946
Likes: 2
N
Member
It is GE, full of stinkn' twins too.

#107183 11/27/04 07:15 AM
Joined: Dec 2000
Posts: 4,295
Member
So, how much wire bending space is required? In the '99 NEC, it's determined by Table 373-6(a)

Only 1-1/2" is required for the size of conductors here if they're #8 or #6, 2" if a #4 or#3. This provides that and more.
That's how it gets listed.
(BTW, these surface enclosures are basically the same design as the semi-flush version, made to fit in the space of a normal 16"OC stud bay)


As for the twin C/B's, these GE combination services are listed for their use, and I've not personally ever had to replace one that's burned up like a Zinsco.

The problem here was not the manufacturer,but the installer that slapped in the 1" PVC without a locknut (it would have pulled the concentric KO out if there was one), and wasn't careful about how he routed his wire to the C/B that really doesn't belong in this panel.(Besides being not listed for the purpose) The GE's have a little cross tab on the bus, and I don't think a CH has the slot to accept it. They won't stab on the bus all the way, so some guys just break off the cross-tabs, throw them in and use the deadfront to hold them in place.

Everything was probably fine until this Turkeylips came along [Linked Image]
Maybe a pool/spa installer that "does it all"?




[This message has been edited by electure (edited 11-27-2004).]

#107184 11/27/04 10:41 AM
Joined: Jun 2004
Posts: 206
C
Member
turkeylips ??? Thats a new one for me. It is fitting though as that Cutler-Hammer 2 pole does not belong there. Also expansion fittings would have worked nicely in this installation. We use them in the northeast due to frost heaving the ground.

Al

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Popular Topics(Views)
338,194 Are you busy
263,614 Re: Forum
243,642 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5