Electricians revenge
0 members (), 205 guests, and 12 robots.
Since there are more than one receptacle on the circuit, it is felt that no receptacle is likely to require more than 15 amps.
Were it a dedicated circuit, with just the one outlet, then it would be necesary to use a 20 amp receptacle.
I understand that's it's allowed by NEC, but everything else the NFPA puts out is so ultra-conservative that it seems bizarre they would allow for so common and easy a way to overload a 15 amp receptacle as to allow a 20amp breaker. It just doesn't seem right.
Unless you're using the bottom of the barrel cheap receptacles, a 15A and a 20A recept are internally the same... (ie. P&S BR15/BR20, Hubbell CR15/20, etc.)
PS... The outlet above is likely older than the invention of the CO/ALR type device. It looks like the old Rodale outlets from the early 60's.
[This message has been edited by Lostazhell (edited 12-02-2005).]
