Will the AHJ accept this installation? #105582 05/04/05 11:52 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
The Type SE grounded service entrance conductor, grounding electrode conductor and all of the equipment grounding conductors are secured to this split bolt.

The MBJ is also installed as required.

The home is still being built in the Albany, NY area and this equipment was not inspected yet?

Do you think that the AHJ will accept this concept?

The work was done by an electrician

[Linked Image]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Will the AHJ accept this installation? #105583 05/05/05 07:26 AM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
With the exception of the EGCs, this would seem to be "ugly but legal", as far as I can see. The split bolt does appear to be the required Cu/Al type, but AFAIK, split bolts are only rated for 2 conductors.

If the EGCs are moved to the neutral/ground bar where they belong, then it might have a chance of passing.

Was there no large hole available on the neutral bar to take the GEC? And it looks like the installer used his teeth to strip the GEC, as well... [Linked Image]

[This message has been edited by NJwirenut (edited 05-05-2005).]

[This message has been edited by NJwirenut (edited 05-05-2005).]

Re: Will the AHJ accept this installation? #105584 05/05/05 11:08 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Here's a full view of this job.

[Linked Image]


Joe Tedesco, NEC Consultant
Re: Will the AHJ accept this installation? #105585 05/05/05 08:14 PM
Joined: Oct 2004
Posts: 803
mxslick Offline
Member
Too rough looking, but might pass.

I think the gutter for the Romex was a good concept, but question the huge wad of wire passing thru the chase nipple (if there is one). Not as far as derating, but just to trace/locate a circuit or its breaker.

And notice all the tripped breakers? Lots of red showing!

(edited for spelling)

[This message has been edited by mxslick (edited 05-05-2005).]


Stupid should be painful.
Re: Will the AHJ accept this installation? #105586 05/06/05 11:45 PM
Joined: Feb 2005
Posts: 219
S
sierra electrician Offline
Member
No matter how you look at it, this is a "Sub Panel" and needs to have a Ground Bus insatlled. The MBJ will be at the Main where it belongs.

Rob

Re: Will the AHJ accept this installation? #105587 05/07/05 12:11 AM
Joined: May 2005
Posts: 706
T
Tiger Offline
Member
I don't see why this is a sub-panel. Anyway, I see it as a violation of 250.64(C) Continuous.

Dave

Re: Will the AHJ accept this installation? #105588 05/07/05 05:32 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Will the AHJ pass this? Who knows they very well might, there are many inspected services that use a split bolt connector in this manner.

I think the question is Should they pass this?

IMO no, the AHJ should not pass this.

Now this does not appear to me to be a sub panel.

I also do not see this as a violation of 250.64(C).

The GEC may be connected anywhere from the weatherhead to the panel.

Quote
250.24(A)(1)General.The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.


What I do see is a 110.3(B) issue as NJwirenut was pointing out.

That split bolt connector is only listed for two conductors not a 'dozen or so'

That 'green' is not insulation, it is green tape covering all the individual EGCs for the branch circuits.

My bet is Joe is also looking for 408.20.

Quote
...Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet.....


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Will the AHJ accept this installation? #105589 05/07/05 05:48 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
408.20 ... Bingo!

Also, this was the main service panel, see the MBJ "Green Screw" upper right.

[Linked Image]


Joe Tedesco, NEC Consultant
Re: Will the AHJ accept this installation? #105590 05/07/05 03:46 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
MX...I hope the breakers are "tripped." That's how they come from the factory. (As a quality control measure, the breakers pass through a magnetic field that trips a good breaker. Those that don't trip are trashed. This is done as one of the last steps before packaging.)

Re: Will the AHJ accept this installation? #105591 05/07/05 08:26 PM
Joined: Oct 2004
Posts: 803
mxslick Offline
Member
renosteinke:

Thanks for the info!! I had always wondered why they arrived tripped from the factory. I had thought it meant they were mishandled in shipping... [Linked Image]


Stupid should be painful.
Page 1 of 4 1 2 3 4

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
andey 2
Popular Topics(Views)
261,266 Are you busy
196,432 Re: Forum
185,701 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3