concentric vs ecentric #10555
06/15/02 01:53 AM
06/15/02 01:53 AM
E
Eandrew  Offline OP
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
I need help in determining the difference (with respect to running an jumper )of concentric vs ecentric knock out. which one requires an additional bonding jumper. which knock does not provide an ground path.

I saw NEC refers to this in services, but what about disconnects in general.

Work Gear for Electricians and the Trades
Re: concentric vs ecentric #10556
06/15/02 08:12 AM
06/15/02 08:12 AM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See Section 250.97 in the 2002 NEC where the same rule can be found concerning the ko's you described.


Joe Tedesco, NEC Consultant
Re: concentric vs ecentric #10557
06/15/02 12:34 PM
06/15/02 12:34 PM
C
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
this is what i understand to be true but maybe someone else can verify this.....
short answer, theres no difference, neither k/o has likely been certified in equipment to carry currents.
250.92 says to bond around both concentric and eccentric knockouts with bonding jumpers at "services" regardless of voltage, then 250.97 says for over 250 volts to ground, metal raceways and cables with metal sheaths that contain any conductor "other than service" conductors have to be bonded same as in 250.92, except for option(1) because that would be bonding equipment to the g.c. on the services load side downstream.
i've used a listed 4 square box with only one eccentric k/o that doesn't need to be bonded around because the locknuts can make good enough contact outside the eccentric ring, but have to be sure its listed for that.
my understanding is that like reducing washers, the k/o's in gutters and panels are never acceptable to carry any currents so they should always be bonded around with bushings and jumpers, except for the type i mentioned above.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008