#10555 06/15/02 01:53 AM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
I need help in determining the difference (with respect to running an jumper )of concentric vs ecentric knock out. which one requires an additional bonding jumper. which knock does not provide an ground path.

I saw NEC refers to this in services, but what about disconnects in general.

#10556 06/15/02 08:12 AM
Joined: Oct 2000
Posts: 2,749
Member
See Section 250.97 in the 2002 NEC where the same rule can be found concerning the ko's you described.


Joe Tedesco, NEC Consultant
#10557 06/15/02 12:34 PM
Joined: Jun 2001
Posts: 196
C
Member
this is what i understand to be true but maybe someone else can verify this.....
short answer, theres no difference, neither k/o has likely been certified in equipment to carry currents.
250.92 says to bond around both concentric and eccentric knockouts with bonding jumpers at "services" regardless of voltage, then 250.97 says for over 250 volts to ground, metal raceways and cables with metal sheaths that contain any conductor "other than service" conductors have to be bonded same as in 250.92, except for option(1) because that would be bonding equipment to the g.c. on the services load side downstream.
i've used a listed 4 square box with only one eccentric k/o that doesn't need to be bonded around because the locknuts can make good enough contact outside the eccentric ring, but have to be sure its listed for that.
my understanding is that like reducing washers, the k/o's in gutters and panels are never acceptable to carry any currents so they should always be bonded around with bushings and jumpers, except for the type i mentioned above.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
Trumpy 11
BigB 4
Popular Topics(Views)
307,114 Are you busy
235,111 Re: Forum
219,246 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5