ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Pull out fuse panel?
by gfretwell. 12/17/18 02:33 PM
Video door bell causing chime activation of coil
by gfretwell. 12/16/18 09:01 PM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 38 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
garage door circuits #102810
12/10/06 11:37 PM
12/10/06 11:37 PM
U
u2slow  Offline OP
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
Large residential garage. 5 garage door openers. All a 1/2hp 120V motors. Three motors have an 8A FLA, and two have a 6A FLA.

It pains me to have to have 5 individual circuits, but I can't seem to find any way around it. 28-206(a) pretty much kills it... the rest of the rule doesn't seem to apply.

Any ideas?

Tools for Electricians:
Re: garage door circuits #102811
12/17/06 01:33 AM
12/17/06 01:33 AM
S
smokumchevy  Offline
Member
Joined: Feb 2003
Posts: 60
Ottawa, Ontario, Canada
Well, as I see it, reading it to the letter you'd have to run 1- 15A circuit to cover your 2-6A openers, and then one each for you other 8A openers, totaling 4-15A circuits.

Now personally, considering this is a 'residential' or 'personal non-commercial' home garage, and seeing that the chances of more than one opener wld be in use at the same time, I'd have no problem myself running only 1 circuit for all. OR 2 circuits and config them as one for the 6A 6A 8A, and one for the other 8A 8A. OR better yet, 1-15A for a 6A & 8A opener, 1-15A for another 6A & 8A opener, and 1-15A for your last 8A opener, totaling 3-15A circuits.

But in the end your really only saving one or two extra runs to conform properly and only you know your or your customers intent of use, so follow your gut feeling and do as you feel comfortable doing.

-Greg


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,274 Are you busy
189,223 Re: Forum
178,910 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.006s) Memory: 0.9428 MB (Peak: 1.0602 MB) Zlib enabled. Server Time: 2018-12-18 15:13:47 UTC