Just wondering what others think.
When doing service upgrades i will run across where theres not enough height on the wall to mount the meter at the prescribe height and have enough area to support the mast.

the first pic raised an eye brow as my inspector told me there should be 4 ft of mast between the top of meter and the highest support bracket.

[Linked Image]


this 2nd pic is one i did to compensate for the lost height. of course this pic is much more work to accomplish


[Linked Image]

[This message has been edited by dougwells (edited 07-18-2006).]

Horizontal Ad
#102665 07/18/06 11:09 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I'm not familiar with this "4 foot rule." I'm interested in where it comes from.

Appendix B, 6-112(4)(c) is a rule about the projection above the roof.

#102666 07/18/06 11:14 PM
Joined: May 2003
Posts: 1,157
Member
I think its an BC Hydro (POCO) requirement

#102667 07/21/06 11:44 PM
Joined: Jul 2005
Posts: 183
J
Member
4 feet of mast between the top of the meter and the highest support?? that means you have four feet to install the three required supports on the wall for the mast. That seems a little odd as a rule, I could see some installs where you had no choice, but imagine if you had 10 feet above the meter until you hit the soffit, all your brackets are grouped in the lower 4 feet. I would Checdouble check that rule again.

#102668 07/22/06 11:33 AM
Joined: May 2003
Posts: 1,157
Member
then we extend the mast with EMT and change the meter hub to a threaded one [Linked Image]
Theres an Adapter to transition from the mast to EMT also.

#102669 07/26/06 11:56 AM
Joined: Jun 2006
Posts: 613
M
Member
From appedix B 6-112 the mast definitions only state that there must be at least 3 supports. 1 at the roof line and 2 on the wall and capeable of supporting a 270 kg cantelever load. The maximim unguyed length above the roof is 1.5 meters. If the mast can support the side load with less than 4 feet below the roof then I think it is OK but maybe the mast cannot normally support such a load with such a large cantelever above the roof and the 4 foot thing arises from that.

#102670 07/26/06 11:56 PM
Joined: Sep 2003
Posts: 200
U
Member
My inpsector pointed out I am lucky to have an intermediate pole at my property line (30' away). Otherwise the cantilever load of the triplex crossing my front street would be too great for the height of my mast. (Green garage door is only about 6'6" high).

[Linked Image from u2slow.gotdns.org]

[This message has been edited by u2slow (edited 07-27-2006).]

Horizontal Ad

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
558,663 Are you busy
432,946 Re: Forum
401,943 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5