0 members (), 708 guests, and 17 robots.
#102627 07/07/06 12:12 AM
MJ2000 Offline OP
Customer wants to use 12kw standby generator
to feed all house(200 amp service) in case
of blackout.Mostly lights,fridge,plugs,etc.
Does rule 08-104(2) apply for this case?
Thanks
#102628 07/07/06 11:49 AM
12 kw is 50 amps at 240 volts so that is the rating of the generator and you can connect 80% of that. If he wants to run the whole house he needs a bigger generator. So what is the solution? Take the most essential loads like the fridge, some lights, any pumps essential to sanitation or flood protection possibly. Add a bit of heat for one room and a few convenience outlets for the wireless phone and a hot plate and you are getting to the limit. The load center must be connected through an approved transfer switch with a source from the regular panel and 1 from the generator. Both sources would have a 50 amp breaker ahead and feed a 60 or 100 amp loadcenter through the transfer switch. The grounding at the generator must be checked to ensure the neutral is not grounded as most transfer switches will have a continuous neutral.
#102629 07/08/06 02:23 PM
MJ2000 Offline OP
The problem is if you want to have all lights
in house and possibillity of using all plugs,in this case you need many circuits to put on
subpanel(plus fridge,subpump,furnace etc).
The easiest way is to install main
disconnecter after meter and transfer switch
(service rated) and connect generator. Customer knows that generator is not big enough for all house(full calculated load) and will take control of load. Generator is protected of overload so that I can't see a problem for this solution.
If customer is not at home in case of blackout generator is big enough for load
remain switched on.
#102630 07/26/06 07:14 PM
Mj it is still a violation to connect a load greater than the generator capacity so the essential circuits must be seperated from the main service and fed via the transfer switch through a load center to 80% of the max rating of the generator.
#102631 07/26/06 09:52 PM
12kw @ 120v is 100 amps, that's all you have so it will not meet the needs of a 200 amp panel. 8-104(2) "the calculated load of a circuit shall not exceed the ampere rating of the circuit".
I think mikesh is correct, you will need a transfer switch and sub panel, I get the impression the owner wants to backfeed the existing panel.