Load Calculations #102481
04/01/06 08:26 PM
04/01/06 08:26 PM
T
teck_ed  Offline OP
Junior Member
Joined: Dec 2005
Posts: 6
thorold
I have a 100 amp 3 phase service commercial building. The customer wants to open a tanning salon with 4 beds. 1 is 60 amp, 220 vac, 2 @ 20 amp 220 vac and 1 is 30 amp 220 vac. Also some lights, plugs and A/C 20 amp 220 vac. Is the 100 amp 3 phase service big enough? Your help is appreciated.

Tools for Electricians:
Re: Load Calculations #102482
04/02/06 09:46 AM
04/02/06 09:46 AM
B
bigrockk  Offline
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
Hello ED
Check out section 8 of the code book paying paticular attention to 8-210 and table 14.These will help you determine your service and feeder sizes.

You will need to know the outside dimensions of the building to calculate a basic load and then you will have to add in all of the "special" loads.
When determing the current draw of a paticular machine or piece of equipment make sure you check the " data plate" on the machine for this info and do not go by the breaker size it is connected to.
Hope this helps.

Re: Load Calculations #102483
04/05/06 08:03 PM
04/05/06 08:03 PM
M
marsbar  Offline
Member
Joined: Apr 2006
Posts: 31
london, ont, canada
Is you 100amp 3ph coming in at 600v? Bigrockk is right you should do a building calc. to be sure.

Re: Load Calculations #102484
04/05/06 11:43 PM
04/05/06 11:43 PM
B
bigpapa  Offline
Member
Joined: Mar 2006
Posts: 81
canada
You dont need to do any demand calculations.

The simple answer is no. Add up the KW for each load and find the total current. Its about 87A just for the beds.

Re: Load Calculations #102485
04/06/06 08:05 AM
04/06/06 08:05 AM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
re bigpapa's reply, you still need to refer to table 14 to establish your basic load, then as 8-210 tells us,"special loads .....based on the rating of the equipment installed with such demand factors as are permitted by this Code." Since your existing service will not be large enough, you still need to get out the calculator to determine the appropriate service feeder size.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,623 Are you busy
186,362 Re: Forum
175,828 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9669 MB (Peak: 1.1044 MB) Zlib enabled. Server Time: 2018-08-19 09:42:22 UTC