re bigpapa's reply, you still need to refer to table 14 to establish your basic load, then as 8-210 tells us,"special loads .....based on the rating of the equipment installed with such demand factors as are permitted by this Code." Since your existing service will not be large enough, you still need to get out the calculator to determine the appropriate service feeder size.