ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
VDE 0100 to introduce AFCIs
by LongRunner. 01/17/18 10:32 AM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
Air Compressor feeder conductor sizing
by Potseal. 01/15/18 09:08 PM
Under carpet cable?
by HotLine1. 01/15/18 09:57 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 18 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Armoured cable and EMT #102310
01/10/06 07:52 PM
01/10/06 07:52 PM
B
bigrockk  Offline OP
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
I work in an industrial plant and we are undergoing renovations in our offices.
A contractor is doing the work and he hired his own electricians to run the conduit for the reno's as I couldn't commit full days to the project as the plant maintenance and equipment breakdowns are my first priority.
All of pipe work for receptacles and switches is 3/4" EMT stubbed up just above what will be the drop ceiling. The part that seems strange to me is they ran BX cable down the pipe and into the device boxes rather than terminating the pipe in a j box and running single conductors.
Does this seem strange to anyone else or am I just outdated? Are there any code violations in regard to doing this? I can't really think of any violations but I have never seen this done before.

Tools for Electricians:
Re: Armoured cable and EMT #102311
01/10/06 10:59 PM
01/10/06 10:59 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
You have to use either a box or a BX to EMT conector like this
http://www.usahardware.com/inet/shop/item/30130/icn/20-067256/halex/15305b.htm

and skin the metal cladding off AC90.None of the cladding can enter the pipe and there has to be a strain relief and of course anti-short.
I've also seen a bx connector to nipple to EMT box connector used to make the transition.
cheers


[This message has been edited by frank (edited 01-10-2006).]

Re: Armoured cable and EMT #102312
01/11/06 07:55 PM
01/11/06 07:55 PM
B
bigrockk  Offline OP
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
Frank,
Thanks for the info and the quick reply.
I am also wondering if you know the code rule that has been violated? I can't seem to pin it down.

Re: Armoured cable and EMT #102313
01/11/06 09:09 PM
01/11/06 09:09 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
For AC90 the inspector will ask you to read rule 12-608 for cable armor continuity and that it be mechanically continuous.
Then rule 12-610 sub-rule (3)for visibility of the bushing...Basicaly they will say it is contrary to these rules so its a defect.Almost the same deal for BX,thats how they rationalize it.
There is no a specific rule but these other rules dictate the installation requirements.

They do not want any of the conductor terminations to take the stress of the cable and should the armor become hot they want to be sure the OCPD clears the fault.
cheers

[This message has been edited by frank (edited 01-11-2006).]

Re: Armoured cable and EMT #102314
01/11/06 11:11 PM
01/11/06 11:11 PM
B
bigrockk  Offline OP
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
12-608 Continuity of Armoured Cable.
The armour of cables shall be mechanically and electrically continuous throughout and shall be mechanically and electrically secured to all equipment to which it is attached.


I think this is the rule that nails it down, as it is definitely not mechanically secure to the pipe.
Thanks again Frank


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,527 Are you busy
180,327 Re: Forum
170,819 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9672 MB (Peak: 1.1040 MB) Zlib enabled. Server Time: 2018-01-17 20:02:02 UTC