Subpanel #102224
10/05/05 07:59 PM
10/05/05 07:59 PM
S
sam_rock  Offline OP
New Member
Joined: Jul 2004
Posts: 5
canada
Hi guys,,,
Can i use NMWU #6 copper to feed a 60 amp subpanel?
Thanks in advace

Tools for Electricians:
Re: Subpanel #102225
10/06/05 10:46 PM
10/06/05 10:46 PM
C
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I'm going to add a little bit to this question.

For the double dagger exception in Table 2 , how is a person to interpret (in relationship to services, feeders and branch circiuts) the term "subservice"?

Re: Subpanel #102226
10/07/05 12:24 AM
10/07/05 12:24 AM
B
bill woods  Offline
Member
Joined: Nov 2001
Posts: 45
isn't a subservice a load centre or subpanel? sam_rock be aware there are restrictions on running nmwu indoors. check with your ahj.

Re: Subpanel #102227
10/07/05 08:37 AM
10/07/05 08:37 AM
C
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
Good point Bill. According to table 19, NMWU has limited use in dry locations. And as such may not be acceptable for a residential sub panel.

I was always taught that the conductors feeding a load center or a sub panel were called feeders.

Re: Subpanel #102228
10/09/05 10:05 AM
10/09/05 10:05 AM
B
bigrockk  Offline
Member
Joined: Jan 2003
Posts: 174
Middle of Canada
Quote
According to table 19, NMWU has limited use in dry locations. And as such may not be acceptable for a residential sub panel.


It seems to me that according to T19 NMWU can be used pretty well any where NMD90 is used, so if we are talking residential (I am assuming single dwelling, and maybe that is my misunderstanding?) Under what
circumstances would NMWU not be acceptable to feed a sub panel, what am I missing?

Quote
For the double dagger exception in Table 2, how is a person to interpret (in relationship to services, feeders and branch circuits) the term "sub service"?

Not something I have really thought about before, I have always interpreted it as any panel/load centre that is feed from the main service.

Re: Subpanel #102229
10/09/05 11:28 AM
10/09/05 11:28 AM
C
CRM  Offline
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
Table 2, column 1 allows a #6 wire to be used at 60 amps, if this is for residential. Its common practice to use NMWU cable to feed detached garages from houses. The only restriction on using NMWU in a residence would be rule 30-408(1). Branch circuit conductors having insulation suitable for 90 degrees celsius shall be used for wiring of ceiling outlet boxes on which a luminaire is mounted except for boxes in wet locations where type NMW or NMWU cables are used.

Re: Subpanel #102230
10/10/05 11:29 PM
10/10/05 11:29 PM
C
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I stand corrected on the table 19 issue.

As far as the double dagger. Big Rock, this is not something I have thought about much, either. According to Sec 0 a circiut feeding a sub-panel is a "Feeder" (services and branch circiuts are also defined). Sub-service is not defined in Sec. 0.

If the definition of "sub-service" includes "feeders", then the answer to Sam-rock's question is "Yes", provided you follow table 19

Re: Subpanel #102231
10/18/05 07:06 PM
10/18/05 07:06 PM
S
sam_rock  Offline OP
New Member
Joined: Jul 2004
Posts: 5
canada
thank you everyone for helpful reply


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,362 Are you busy
187,292 Re: Forum
176,643 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9915 MB (Peak: 1.1524 MB) Zlib enabled. Server Time: 2018-09-22 05:22:19 UTC