I have ATS Service Entrance HS Type Transfer Switch Model 004945-1,200 Amp, 250 Volts Generac Power system, this switch has service disconnect circuit breaker. I would like to install this switch between meter socket and main panelboard ( supply side of existing consumer's service entrance) for Standby generator.
Is this switch approved for service entrance use? (owner's manual said "this transfer switch is suitable for use as service entrance equipment) I live in Toronto.
Thanks
|
|
|
|
Joined: Dec 2001
Posts: 444
Member
|
|
|
|
|
Joined: Jun 2005
Posts: 17
OP
Member
|
Thanks Sandro, this is very important for me and because of that I would like Toni Moscioni's opinion.
Thanks
|
|
|
|
Joined: May 2001
Posts: 144
Moderator
|
There are some transfer devices bearing markings such as “Suitable for service use” which is an American NEC marking not applicable in Ontario. Manual transfer devices approved for service entrance use in Ontario shall be approved to CSA Standard C22.2 No 4, shall be marked “Suitable for use as service equipment” (note the subtle difference in wording), shall meet the OESC definition of a Service Box (switch & fuse, or circuit breaker), and shall have the neutral assembly bonded to the enclosure with provision for separate connections of the line and load neutral conductors and the service ground conductor.
A pole top switch may also be located on the supply side of a consumer’s service entrance provided it is installed in accordance with OESC Section 75.
Under no circumstances shall a generator be connected to any portion of a wiring system except where it is connected through a transfer device that makes it impossible for the generator to feed back into the normal power supply. [Ontario Electrical Safety Code (OESC) 6-106, 14-612, 75-608].
Where a double throw transfer device is mounted at a service entrance, the transfer device shall be located on the load side of the service entrance switch [OESC 75-608 (3)(d)], except as follows:
A transfer device may be located on the supply side of an existing consumer’s service entrance at a building provided:
· it is approved for service entrance use [2 -034].
· the consumers service ground conductor connection is relocated to the transfer device and the neutral bond screw or jumper in the existing service box is removed. [10- 204(1)(a)(b)(d)]
· a bond conductor is present between the new transfer device and existing service equipment. [10-400]
· this transfer switch shall be treated as the consumers service box for code interpretation purposes.
Tony Moscioni Electrical Inspector Electrical safety Authority
|
|
|
|