ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Welded Copper Connections
by gfretwell. 04/17/19 10:03 PM
Water heater calculationsSo when I count calculati
by watersparkfalls. 04/13/19 12:43 PM
Health Canada Electric Construction heaters recall
by dougwells. 04/12/19 01:22 AM
Burning out of return(white) side of 120volt rec
by richard. 04/08/19 07:12 PM
Interesting Knob & Tube setup
by Texas_Ranger. 04/03/19 12:49 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 9 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
incoming service #102077
12/13/04 12:57 PM
12/13/04 12:57 PM
G
GETELECTRIC  Offline OP
Member
Joined: Oct 2003
Posts: 172
toronto canada
I have an incoming service 600v 100amp going to a 3 storey commercial bldg, it is being fed overhead, my question is this, can i run the conduit though the parking garage ceiling 50'to the electrical room into the main then into the meter center.Something tells me i can,t but if i do underground from the weatherhead to the electrical room that is ok?

Tools for Electricians:
Re: incoming service #102078
12/14/04 08:48 PM
12/14/04 08:48 PM
C
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
That "something" that is "telling you", might be 6-208. Underground is OK but 50 ft through the parkade is not allowed.

Re: incoming service #102079
12/15/04 07:11 PM
12/15/04 07:11 PM
T
Tony Moscioni  Offline
Moderator
Joined: May 2001
Posts: 144
CANADA
Where judgement required about "as close as practicable", the following may be used for
guidance on the maximum length of run:

(i) 1.5 m into rooms or areas of combustible construction; or

(ii) 7.5 m into other areas provided:
„h the wiring method is rigid conduit, electrical metallic tubing (EMT) or a cable
with a continuous metal sheath or interlocking armour, (No PVC greater than
625mm2 as per Building Code), and
„h the conduit or cable is mechanically protected where it is within 2 m of the floor.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,412 Are you busy
190,664 Re: Forum
180,384 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.004s) Memory: 0.9505 MB (Peak: 1.0751 MB) Zlib enabled. Server Time: 2019-04-18 15:18:57 UTC