#101887 12/22/03 03:48 PM
Joined: Oct 2003
Posts: 172
G
Member
we have a set of drawings that does not show what size of grding for a 225 kva 600-120/208
transformer.our best guess is table 17 going with 3/0

Joined: Oct 2003
Posts: 147
C
Member
Getelectric: It sounds like you are looking for 10-204(2), and applying it to a delta/wye transformer. Table 17 and 3/0 would be the correct. However the last phrases and their reference to 4-022 confuse me. I believe the 4-022 reference would apply to a wye primary.

[This message has been edited by crash (edited 12-22-2003).]