Satellitte Grounding #101632
04/17/02 07:58 AM
04/17/02 07:58 AM
L
Lawrence  Offline OP
Junior Member
Joined: Nov 2001
Posts: 7
Halifax,NS,Canada
Figure 54-922 (Grounding of Antennas) shows a dish being grounded by a #6 to the grounding electrode of a residential application.In a hi-rise commercial application this may not be practical.Is it acceptable to to run the #6 to the nearest panelboard and ground it to the panel with a mechanical lug?
The figure also shows a bonding conductor between the lightning arrester and the panelboard.What size conductor should be used?

Thanks

Tools for Electricians:
Re: Satellitte Grounding #101633
04/17/02 06:57 PM
04/17/02 06:57 PM
T
Tony Moscioni  Offline
Moderator
Joined: May 2001
Posts: 144
CANADA
Lawrence,

You can install the grounding conductor to the nearest accessible location on the following:

The building or structure grounding electrode system.

The grounded interior metal water piping system.

The power service accessible means external to enclosures.

The metallic power service raceway.

The service equipment enclosure.

Bonding of Electrodes

A bonding jumper not smaller than No.6 copper or equivalent shall be connected between the radio and television equipment grounding electrode and the power grounding electrode system at the building or structure served where separate electrodes are used.
The grounding electrode conductor or the grounding electrode conductor metal enclosures.

Antenna masts must be grounded to the same grounding electrode used for the electrical system of the building. This is necessary to ensure that all exposed, non-current carrying metal parts are at the same potential. In many cases, masts are incorrectly connected to the conveniently located vent pipers, metal gutters, and downspouts. This could create potential differences between lead-in conductors and various metal parts located in or on buildings, resulting in possible shock and fire hazards.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,645 Are you busy
188,780 Re: Forum
178,497 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.005s) Memory: 0.9435 MB (Peak: 1.0624 MB) Zlib enabled. Server Time: 2018-11-21 02:20:07 UTC