1 members (Scott35), 187 guests, and 25 robots.
I have a bias in favor of christie boxes being place next to the poles for the following reasons:
1) There is seldom enough room in the light pole, or the pathetic little handhole in the pole, to work with the larger wires often used for these long runs;
2) Running wires directly to the poles greatly complicates replacement of a pole that has been damaged. With a box, at least, you can isolate the one pole easily, and remove the exposed wires;
3) Poles are getting crowded, with other cables ... speakers, cameras, convenience receptacles, etc.; and,
4) having the wires in the poles greatly complicates future replacement pulls of wire.
This still leaves room for some future re-paving job to cover up the boxes, but you can't idiot proof everything (they keep coming out with better idiots [Linked Image] )
Reno I agree with your approach with one exception:
Usually they can't install these types of cables in poles without violating the NEC. The receptacles ok, but other cables probably violate sections in chapter 7 and 8 of the code that don't allow power and non-power cables in the same raceway and the light pole is now considered to be a raceway.
[This message has been edited by George Little (edited 02-10-2007).]
George Little
George, I wasn't saying it was right [Linked Image] , just acknowledging reality.
I should also point out that I was not saying that code mandated my method in any way. I just wanted to show that "code minimum" might not be very wise in this instance.
Okay Reno. Hope your not offended because I always enjoy your input.
George Little
No offense at all George. I also appreciate your take on things .... even when I cheat!
Is the pole a raceway, though, or is it considered a listed fixture?
Steve- Look at 410.15(B).
George Little
Steve, there is some debate on that point. UL's answer depends, in part, on the length of the pole.
aldav53 Offline OP
( but other cables probably violate sections in chapter 7 and 8 of the code that don't allow power and non-power cables in the same raceway and the light pole is now considered to be a raceway.)
You could run different cables in the same raceway if the insulation voltage rating on it was high enough, correct?
Cable jackets are separation. If you were snaking power in a pole with other circuits you could use something like MC in that segment of the pole.