Conductors in Parallel #10107 05/31/02 12:32 AM
Joined: Jan 2002
Posts: 324
A
arseegee Offline OP
Member
Is there a code stating the maximum number of conductors allowed to be paralleled. I know 1/0 is minimum size but found no limit on how many. I want to use four 350KCM per phase instead of two 1000KCM. Kinda tough to work that fat stuff into the bottom fed switchgear.

Work Gear for Electricians and the Trades
Re: Conductors in Parallel #10108 05/31/02 01:27 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
Four conductors per phase can be used under NEC 310-4, if the equipment is intended for 4 cdr/ø. Keep lengths equal and similarly routed for each group. If 1000kcmil is specified and there’s code-adequate bending space, use it! Won’t kill you.

Re: Conductors in Parallel #10109 05/31/02 05:06 PM
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
I don't think there is a Maximum number as long at the terminations are made to accept the number of the parallel conductors.

Going from a bus to a bus I would think is virtually unlimited.

To devices such a Circuit Breakers the available (listed) lug pattern for that CB would be the determining factor.

Re: Conductors in Parallel #10110 05/31/02 08:40 PM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
I don't believe their is a maximum # of parallel conductors, as long as they meet the conditions of 310.4 ('02), or 310-4 ('99)

Re: Conductors in Parallel #10111 05/31/02 09:53 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
I have never heard of a maximum. The more you do the harder it gets to keep them all "the same length" I have had the pleasure [said with much sarcasm] of terminating 12 runs of 500MCM paralleled myself. (And 10 runs of 600 MCM come to think of it) It is really not that bad IF you have sufficient room and you realize you are not going to finnish before lunch the day you start. (you probably won't finnish before lunch the following day either!)


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
277,354 Are you busy
211,136 Re: Forum
198,156 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3