ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Questioning the electrical norms
by HotLine1 - 03/04/21 12:35 PM
Lock-down Thread
by gfretwell - 03/03/21 12:38 PM
Northern Tool Recalls Powerhorse Generators
by Admin - 02/25/21 09:49 PM
You will never guess
by gfretwell - 02/25/21 07:48 PM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
0 registered members (), 22 guests, and 19 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Ranges #100991 01/25/07 07:15 PM
Joined: Jan 2007
Posts: 59
D
dilydalyer Offline OP
Member
In the 2002 code,is T220.19 for load calculations....I have a gut telling me you can set your overcurrent prot. and wire size by this table......

2017 / 2014 NEC & Related Books and Study Guides
Re: Ranges #100992 01/28/07 06:26 AM
Joined: Nov 2005
Posts: 31
J
jdo1942 Offline
Junior Member
This section of the code is for multiple groups of ranges. It is the most confusing part of the code in My opinion. You must use all three columns. It is not like dryers that run a percentage on the total number. To use this table it takes a bit figuring out

Re: Ranges #100993 01/28/07 10:09 AM
Joined: Jan 2007
Posts: 59
D
dilydalyer Offline OP
Member
When I posted this message I meant to say GUY instead GUT....sorry.I would appreciate input on this...thanks jdo.

Re: Ranges #100994 01/28/07 10:34 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
This was posted previously last week and I responded but I'm not sure what I said was very definitive. I have since asked around and looked at the code again and here's what I belive the code says:
220.19 (2002) and 220.55 (2005) and their associated tables are for calculating the load(s) for branch circuits, feeders or services.

The other code reference 210.21(B)(4) tells us that we can size the receptacle based on 220.19 ('02) or 220.55 ('05) so if we size the receptacle using this approach we more than likely would size the rest of the circuit this way.

Also look at Note 4 for Table 220.19 ('02) or 220.55 ('05) and you get a sense of how a branch circuit for a single range is sized.

The code also says that for a 12KW range the receptacle can not be less than 40a.

8000/240=33.3 but we must use a 40a. wire and overcurrent and I think a 50a. receptacle. I don't believe they make a 40a. receptacle

I would like to hear from others as to my error or lack thereof.

[This message has been edited by George Little (edited 01-28-2007).]


George Little
Re: Ranges #100995 01/28/07 11:35 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Interesting:
12000 KW range would be calculated as following for load.

Start with 8000 and add 1600 (based on Note 1)=9600.

9600/240 = 40a.


George Little
Re: Ranges #100996 01/28/07 12:12 PM
Joined: Jan 2007
Posts: 59
D
dilydalyer Offline OP
Member
tks...give me some more studying

Re: Ranges #100997 01/28/07 06:20 PM
Joined: Jan 2007
Posts: 59
D
dilydalyer Offline OP
Member
But don't u think I could not treat the only range in the house,let's say a 12kw,as an 8kw as far as wire and breaker size?

Re: Ranges #100998 01/28/07 07:23 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Yes


George Little

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,689 Are you busy
209,610 Re: Forum
196,959 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3