grounding electrode conductor #100787 01/02/07 10:39 PM
Joined: Apr 2002
Posts: 189
T
triple Offline OP
Member
250.56 and 250.64(F):
If 25 ohms or less is not achieved with one ground rod, and a second one is added, do the two need to be tied together with the same continuous wire back to the common bonding point (panel)? I realize that an irreversible connection could be used but is there any reason that a separate wire couldn't be run from each of the two rods back to the panel? BTW, Wisconsin requires two ground rods no matter what.

2017 / 2014 NEC & Related Books and Study Guides
Re: grounding electrode conductor #100788 01/02/07 10:52 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
The first rod is your "grounding electrode." The second is a "supplementary electrode" It can be attached with a separate wire to the first rod.

Re: grounding electrode conductor #100789 01/03/07 05:28 PM
Joined: Apr 2002
Posts: 189
T
triple Offline OP
Member
If the first electrode does not meet the 25 ohm maximum requirement then the second electrode is not simply a "supplementary grounding electrode" is it? Also, since Wisconsin requires two in every case then the second one would never be supplimental (imo). Renosteinke, are you suggesting that the wire from the second rod can be simply bolted to the first rod without an irreversible connection to the first rod's conductor? How about 250.64(C)?

Thank you.

Re: grounding electrode conductor #100790 01/03/07 05:47 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Triple, the conductor from one electrode to another is not a GEC.

The GEC runs from the panel to some point of the grounding electrode system.

The conductors that connect multiple grounding electrodes together are bonding jumpers. 250.64(C) does not apply to these bonding jumpers.

Here is a picture from the handbook showing different ways of connecting the grounding electrode system together.

[Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: grounding electrode conductor #100791 01/04/07 08:36 AM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
Jon, the second rod would be supplemental, not supplementary.


Ryan Jackson,
Salt Lake City

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,514 Are you busy
209,410 Re: Forum
196,800 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3