I know you can't run AC difference phases in different pipes but what about 125 volt DC. Hot =one metal pipe Ground = another metal pipe from metal box to metal box in EMT coming off a large batterey bank.
|
|
|
|
Joined: Jul 2004
Posts: 10,015 Likes: 37
Member
|
I don't think it would get hot but I bet you could stick your Kliens on the box and the magnetism would hold them there.
Greg Fretwell
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
If the circuit is covered by the NEC 300.3(B) applies and requires the circuit conductors to be run together unless one of the exceptions fits.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2005
Posts: 826 Likes: 1
Member
|
Are you sure that you are dealing with HOT and GROUND? All of our strings are plus and minus and floating with respect to ground. Some of our apps use ground detectors while we just check others during monthly battery checks. Joe
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
Joe Your right Plus and Minus But working with AC 99% of the time I used the wrong term.
|
|
|