Garage re-bar bonding #100661
12/08/06 09:20 PM
12/08/06 09:20 PM
K
kencr  Offline OP
Member
Joined: Jul 2004
Posts: 35
Southern, NJ USA
I am actually building my own garage, and I have not bonded rebar in a footing before .. most times it is done by the concrete crew ?? I assume that .. not sure.

Any way ... what type of clamp is approved for that ? And what size copper wire ? # 6 bare I am guessing. The garage will have a 100 amp sub panel feed from the house panel.
Thanks for your replies

2017 / 2014 NEC & Related Books and Study Guides
Re: Garage re-bar bonding #100662
12/08/06 09:26 PM
12/08/06 09:26 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
4ga solid and any clamp listed for burial in concrete and connection to rebar. The bronze one they use in pools is common and Erico has a bronze acorn that works


Greg Fretwell
Re: Garage re-bar bonding #100663
12/09/06 06:12 AM
12/09/06 06:12 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
We use bare stranded, much easer to work with.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Garage re-bar bonding #100664
12/09/06 09:41 AM
12/09/06 09:41 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
gfretwell,
Quote
4ga solid and any clamp listed for burial in concrete and connection to rebar.

Why #4?
Don


Don(resqcapt19)
Re: Garage re-bar bonding #100665
12/09/06 04:21 PM
12/09/06 04:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
250.66(B)Connections to Concrete-Encased Electrodes. Where the grounding electrode conductor is connected to a concrete-encased electrode as permitted in 250.52(A)(3), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 4 AWG copper wire.


Greg Fretwell
Re: Garage re-bar bonding #100666
12/09/06 05:03 PM
12/09/06 05:03 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,271
Fullerton, CA USA
But that doesn't say that it cannot be smaller than #4, only that it needn't be larger.

Re: Garage re-bar bonding #100667
12/09/06 06:14 PM
12/09/06 06:14 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
I agree but when you are casting something in concrete for your own house, why cheap out?
By the time you add physical protection for a smaller size you probably haven't saved any money anyway.


Greg Fretwell
Re: Garage re-bar bonding #100668
12/09/06 08:37 PM
12/09/06 08:37 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Another reason to go for #4. It seems to fit in a portion of this code between (*) pysical damage, and severe physical damage.

Quote
250.64(B) Securing and Protection from Physical Damage. A grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. A 4 AWG copper or aluminum or larger conductor shall be protected if exposed to severe physical damage. (*) A 6 AWG grounding conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; otherwise, it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Grounding conductors smaller than 6 AWG shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor.


[This message has been edited by e57 (edited 12-09-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Garage re-bar bonding #100669
12/10/06 01:15 AM
12/10/06 01:15 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The code would permit a #8 GEC for this application. The #4 is the maximum required by the code for a GEC to a concrete encased electrode, but Table 250.66 applies and the use of smaller conductors is permitted. The smaller wire may not require and physical protection. It could be stubbed up in a stud space and run to the panel. If there is a wall finish no additional protection would be required.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,678 Are you busy
186,422 Re: Forum
175,901 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.004s) Memory: 1.0030 MB (Peak: 1.1723 MB) Zlib enabled. Server Time: 2018-08-21 17:44:17 UTC