406.8(D) #100422
11/18/06 01:28 PM
11/18/06 01:28 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
iwire--since you brought up 406.8(C) in another thread, I read (D) and am slightly unsure what 'standpipes of floor receptacles..' means.

Insight please...

2017 / 2014 NEC & Related Books and Study Guides
Re: 406.8(D) #100423
11/18/06 01:47 PM
11/18/06 01:47 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Steve I really do not know.

I'll take a guess it is a older code rule for some sort of receptacle box supported on a pipe nipple out of a threaded floor system like walker duct.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 406.8(D) #100424
11/18/06 01:53 PM
11/18/06 01:53 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Steve, it could be something similar to the receptacle below as Bob mentions.

[Linked Image]

Roger

Re: 406.8(D) #100425
11/18/06 10:01 PM
11/18/06 10:01 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
How in the heck do you wire that beasty?

Larry C

Re: 406.8(D) #100426
11/19/06 10:56 AM
11/19/06 10:56 AM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
There must be some long wires trailing from the periscope.


Earl
Re: 406.8(D) #100427
11/19/06 03:30 PM
11/19/06 03:30 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Larry and Earl, we found these in a university remodel. At first I wasn't sure either, but we found that they were mounted to floor duct through a nipple and the 1" RMC coupling that you see in the picture.

You can see the two screws that hold the top canopy on the fitting.

When the top is removed the devices can be wired (by the way this is a duplex receptacle, there is one on the other side too) and then the wires pulled back as the devices are fit back into their place in the fitting.

Roger

Re: 406.8(D) #100428
11/27/06 08:29 PM
11/27/06 08:29 PM
S
Steve T  Offline OP
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
If that type of install is what is meant, then my question is--
How high off the floor does a receptacle have to be mounted before it is not a floor receptacle?

Re: 406.8(D) #100429
11/27/06 09:14 PM
11/27/06 09:14 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Beats me.

Roger

Re: 406.8(D) #100430
11/27/06 10:06 PM
11/27/06 10:06 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
IMHO If it's not in the floor then it's not a floor receptacle. If I'm the inspector, I'm just like the umpire- is it a ball or a strike, is it a floor receptacle or is not a floor receptacle.


George Little
Re: 406.8(D) #100431
11/28/06 06:01 PM
11/28/06 06:01 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
And to think I tossed about 12 of them out!!!

Should have saved at least one, but alas...to late.

As to floor recept...I doubt it.

John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,149
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,163 Are you busy
189,155 Re: Forum
178,833 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.004s) Memory: 1.0087 MB (Peak: 1.1844 MB) Zlib enabled. Server Time: 2018-12-12 12:54:44 UTC