0 members (),
1,495
guests, and
7
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Jul 2004
Posts: 35
OP
Member
|
We have a boat load of 12-4 mc cable which we would like to use up. It was bought at an auction. One thing we could use it for ( I think ) is to run two 2 pole 208 volt circuits to one location. Would this be allowed by code ?
Black - White one 208 circuit
Blue - Red one 208 circuit
Green shared ground.
Yes ?? No ?? Maybe ??
Thanks
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
200.7(C)(1) allows the use of the white in a cable assembly for an ungrounded conductor if you remark it.
So yes you can run two 208 circuits.
However when I see 12/4 I am thinking one multi wire branch circuit.
Black A
Red B
Blue C
White N
[This message has been edited by iwire (edited 11-12-2006).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Jul 2004
Posts: 35
OP
Member
|
iwire
Yes I use it for that also.
We do a pizza chain that has two 208 volt ovens. 4 -11/16 box mounted oven hood with one 12-3 drop cord to each oven. The 12-4 will work great. Just one wire to j box.
Thanks for your input
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Sounds like a great use of 12/4 MC
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Jan 2005
Posts: 5,485 Likes: 5
Cat Servant Member
|
More then three current-carrying conductors... did you de-rate? ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif)
|
|
|
|
|
Joined: May 2005
Posts: 706
Member
|
I thought you aren't allowed to remark small guage branch circuit wiring.
Dave
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Tiger as a general rule you can not.
However there are some exceptions for the white in cable and cord assemblies.
You can find these in 200.7
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: May 2005
Posts: 706
Member
|
200.7(C)(3)?
Thanks iwire.
Also, I thought the 208 volt leg (of a delta 3PH) is only to be used for 3 phase, not single phase.
Dave
|
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
Dave The installation that people seem to be talking about here is with wye connected three phase were the voltage to ground is the same on all three phases.
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
Posts: 2,724
Joined: October 2000
|
|
|
|
|
|