#100330 11/12/06 08:27 AM
Joined: Jul 2004
Posts: 35
K
kencr Offline OP
Member
We have a boat load of 12-4 mc cable which we would like to use up. It was bought at an auction.
One thing we could use it for ( I think ) is to run two 2 pole 208 volt circuits to one location.
Would this be allowed by code ?

Black - White one 208 circuit

Blue - Red one 208 circuit

Green shared ground.

Yes ?? No ?? Maybe ??

Thanks

Horizontal Ad
#100331 11/12/06 08:51 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
200.7(C)(1) allows the use of the white in a cable assembly for an ungrounded conductor if you remark it.

So yes you can run two 208 circuits.

However when I see 12/4 I am thinking one multi wire branch circuit.

Black A

Red B

Blue C

White N



[This message has been edited by iwire (edited 11-12-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#100332 11/12/06 08:57 AM
Joined: Jul 2004
Posts: 35
K
kencr Offline OP
Member
iwire

Yes I use it for that also.

We do a pizza chain that has two 208 volt ovens. 4 -11/16 box mounted oven hood with one 12-3 drop cord to each oven. The 12-4 will work great. Just one wire to j box.

Thanks for your input

#100333 11/12/06 09:15 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Sounds like a great use of 12/4 MC


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#100334 11/12/06 12:48 PM
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
More then three current-carrying conductors... did you de-rate? [Linked Image]

#100335 11/12/06 03:01 PM
Joined: May 2005
Posts: 706
T
Member
I thought you aren't allowed to remark small guage branch circuit wiring.

Dave

#100336 11/12/06 03:06 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Tiger as a general rule you can not.

However there are some exceptions for the white in cable and cord assemblies.

You can find these in 200.7


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Horizontal Ad
#100337 11/12/06 03:18 PM
Joined: May 2005
Posts: 706
T
Member
200.7(C)(3)?

Thanks iwire.

Also, I thought the 208 volt leg (of a delta 3PH) is only to be used for 3 phase, not single phase.

Dave

#100338 11/20/06 02:44 PM
Joined: Mar 2001
Posts: 345
T
Member
Dave
The installation that people seem to be talking about here is with wye connected three phase were the voltage to ground is the same on all three phases.


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
davey 1
Popular Topics(Views)
554,300 Are you busy
428,605 Re: Forum
398,659 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5