Thanks Roger- You beat me to the punch. I was looking it up when your post came through.
George Little
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Thanks George and Roger. BTW removing paint may lead to rust problems in the future. Always repaint over the bonded connection after it's all terminated and tightened. The removal of paint is required by 250.12 if it is inhibiting the connection. So IMO if reducing washers or chase nipples are used the paint would have to be removed to ensure grounding continuity.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Hello George and Iwire, I know one of you would have posted the UL info if I hadn't. This is one situation where I would not argue with an inspector if he did not accept it even though UL says it is safe. As a matter of fact, it wouldn't be an issue because I wouldn't do it or let an employee do it. Roger
|
|
|
|
Joined: Jun 2005
Posts: 821
OP
Member
|
Thanks for all the insight guys. Seems to me that it's in fact a code-worthy installation, but not a preferred method. It's good to know the difference.
|
|
|
|
Joined: Jul 2006
Posts: 272
Member
|
Sounds like either a green wire EGC bond would be required in this installation or replace the chase nipple with a close nipple and use two locknuts (and maybe a bushing). Hello all, just curious as to what earlydean said in the above. I'm clear with replacing the chase nip' with a close nip' and locknuts, but, what method would you use to if you were to leave the install as is, and just bond the LB? One way I can see is run a seperate EGC from the panel to the first pull box or enclosure from the LB, and bond there. How else could it be done? Or am I thinking to much into this?? Luke
Luke Clarke Electrical Planner for TVA.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I can see no reason why a chase nipple 'wrench tight' into an LB would not provide a good bond to an enclosure with the paint removed.
If it made the inspector happy I would put a locknut backward on the chase before installing it into the enclosure.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
Many a chase nipple I have installed wrenchtight into an LB still rattles against the enclosure. There is no way this is providing the "effective ground fault current path" as required by 250.4(A)(5).
The UL listing of reducing washers as a proper ground, sticks in my craw. I will have to digest this for awhile. UL does add: "where installed in accordance with" the NEC.
250.96(A) requires: Metal parts are to be "effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them. Any nonconductive paint, enamel or similiar coating shall be removed" or replaced with grounding fittings.
Earl
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
I have to agree with Earlydean..... I'm OK with a chase nip with locknuts. Some chase nips around here have nice rounded shoulders, so there's no way they would be acceptable.
Still thinking on the derating thing....???
John
John
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
It just isn't that much work to put a locknut between the enclosure and the LB, LL, LR. Once that is wrench tight against the outside of the enclosure I'd call it good.
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|