Light Pole Grounding #100287
11/08/06 05:20 PM
11/08/06 05:20 PM
Z
Zapped  Offline OP
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Hey Everybody,

I'm arguing with a low-ball lighting installer about the need for poles to be grounded as well as the luminaires on 12' parking lot lights. The installer seems to think that the mechanical link between the pole and the luminaire is sufficient, so only the luminaire needs to be grounded. I call BS and reference 410.15 (specifically, 410.15(B)(5)) and feel that the code specifies that any metalic pole, 8' or higher, needs to be bonded to ground using the grounding bolt welded to the inside of the hand hole, and using the manufacturer-supplied (and UL listed) gounding hardware. The luminaire, of course, must be grounded ALSO.

My logic is that if, for some reason (corrosion, a hit from a moving truck, etc.), the luminaire becomes detached from the pole, or the mechanical link becomes comprimised in any way, the pole then becomes a possible conductor when/if a fault occurs. Add one barefooted kid leaning on the pole, and we have a tragedy that could have been easily avoided.

BTW, this guy came in to one of the communities that I service and underbid my company on the pole replacements by using "immigrants of questionable legality" to perform the work for him. There was never, to my knowlege, a certified or licensed electrician on site during the entire process. And yes, I may be a little biased in my motives on this issue.

Does anybody think that I'm out of line on this, or am I right? Are there any inspectors here that have run across this issue and made the call either way?

Thanks in advance for your input.

2017 / 2014 NEC & Related Books and Study Guides
Re: Light Pole Grounding #100288
11/08/06 05:59 PM
11/08/06 05:59 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Zapped, I agree with you, 410.15(B)(5)is mighty clear in requiring the pole to be bonded to an EGC.

Roger

Re: Light Pole Grounding #100289
11/08/06 06:39 PM
11/08/06 06:39 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
Well, the way I see it, even if it was not required to be bonded, The bonding conductor is present and running right past the bonding stud up to the fixture, so why not just take the extra 30 seconds and bond the pole anyway. For the time and material it might take, its peanuts and
" cheap insurance" compared to what the price may be if someone were to get hurt or killed because the pole somehow became hot.

A.D

Re: Light Pole Grounding #100290
11/09/06 08:20 AM
11/09/06 08:20 AM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Zapped:
YES, poles MUST be bonded. This discussion was recently had regarding a "fail" sticker I posted on a site lighting project.

John


John
Re: Light Pole Grounding #100291
11/09/06 11:08 AM
11/09/06 11:08 AM
Z
Zapped  Offline OP
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Thank you gentlemen, it's nice to have some back-up when you know you're right.

It's difficult to beleive what people will argue with you about sometimes.

BTW, sorry for double posting Roger. Thanks for handling that!

Re: Light Pole Grounding #100292
11/09/06 03:10 PM
11/09/06 03:10 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
As a design issue I would like to see the bonding conductor being a bit longer than the circuit conductors so it would break last in a collision.


Greg Fretwell
Re: Light Pole Grounding #100293
11/09/06 03:54 PM
11/09/06 03:54 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Gfretwell:
Sounds plausable.....
Most of the impacts I have dealt with have resulted in some spectacular fireworks; either upon impact, or the 'maintenance guy' trying to reset the 3-pole cb.

John

[This message has been edited by HotLine1 (edited 11-09-2006).]


John
Re: Light Pole Grounding #100294
11/09/06 04:30 PM
11/09/06 04:30 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Zapped, no need for an appology.


Roger

Re: Light Pole Grounding #100295
11/10/06 10:57 AM
11/10/06 10:57 AM
Z
Zapped  Offline OP
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
gfretwell: I wholeheartedly agree with the extra ground wire length.

I've been the guy to go out a secure the sites after poles have gone down, and more than once I've found the wire over extended to the point of failure, and have found more than one has become a 4" X 4"X 20' steel conductor. I've always been glad that I found it before a someone else.

Around here, it's becoming a real problem. So called "lighting" speciallty contractors are entering into the market and are practicing predatorial bidding to get into a job, then using unqualified labor in order to turn a profit on an impossibly low bid. The result? The customers get what they pay for. And IMHO, it's scary, and it will not end well.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,116 Are you busy
185,577 Re: Forum
174,891 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 14 (0.004s) Memory: 1.0030 MB (Peak: 1.1699 MB) Zlib enabled. Server Time: 2018-07-18 20:05:35 UTC