#100026 - 10/05/06 06:12 PM A Code compliant installation?  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Air conditioning condensing unit has a minimum ampacity rating of 18 amps.

A maximum over current protection device rating of 30 amps.

A 60 amp rated non-fused diconnect is used and installed in a readily accessible location.

14 AWG wire is run to the disconnect, and then #14 THWN to the condensing unit.

A double-pole 30 amp circuit breaker is installed at the panel.

Is this an NEC compliant installation?


2017 / 2014 NEC & Related Books and Study Guides

#100027 - 10/05/06 06:44 PM Re: A Code compliant installation?  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Absolutely Green Sticker time.


George Little

#100028 - 10/05/06 07:31 PM Re: A Code compliant installation?  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
I need some clarification on this one.

How can you use a 30a breaker to protect 14g wire?

heck I guess I need to know how 14-2 supports 18a aswell.

[This message has been edited by Trick440 (edited 10-05-2006).]


Shake n Bake

#100029 - 10/05/06 07:41 PM Re: A Code compliant installation?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I agree with George.

Trick first off 14 AWG is rated anywhere from 20 to 25 amps depending on the insulation and terminations.

On typical branch circuits 240.4(D) requires us to use a 15 amp over current device.

However for HVAC units 240.4(G) applies and we can use 14 AWG up to the rating in 310.16 and the short circuit and ground fault protection can be as allowed in 440.6


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#100030 - 10/05/06 07:59 PM Re: A Code compliant installation?  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Can't wait to pull this one on my boss.. lol.

Thank you for the code refs. and explanation.


Shake n Bake

#100031 - 10/05/06 08:24 PM Re: A Code compliant installation?  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Trick, this is exactly why I posted this. I did an over/ under split-system A/C install today and was talking to the HVAC contractor. He saw me looking at the specs on both CU's and told me, "just run a 30 amp 10/2 wire."

So I said, "ok, but I could really just run 14 wire and it'd be ok by NEC standards."

He says, "I've never heard of that so don't so it."

^^
(this coming from the HVAC guy, not an electrician)

Of course, the better install is to run the maximum size wire and the maximum size OCPD, I'm sure most would agree. But the point is, it can be done and pass inspection, and damn it felt good to hold my own in this discussion.

Thanks ECN!


#100032 - 10/05/06 09:10 PM Re: A Code compliant installation?  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Ron:
Ya did good! Just keep watching the mfg nameplates. Only other consideration could possibly be voltage drop, dependent on the run. That's my opinion, when ya cut it close.

John


John

#100033 - 10/05/06 11:12 PM Re: A Code compliant installation?  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Thanks John!


#100034 - 10/06/06 12:44 AM Re: A Code compliant installation?  
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
Most of the mini split systems I have done will list the max fuse or circuit breaker, and the minimum ampacity of the wiring. What I've noticed is they tend to want to protect thier machines from overworking and usually exceed code a bit on the minimum ampacity labeling. Code says go with what is on the label.


#100035 - 10/06/06 09:09 AM Re: A Code compliant installation?  
mountainman  Offline
Member
Joined: Jan 2002
Posts: 54
Richmond Va. U.S.A.
iwire, what about 240.6? In order for this to be code compliant you would need a 25 ampere breaker to comply with 240.4(B). IMHO
thanks Joe


Page 1 of 2 1 2

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.8174 MB (Peak: 0.9942 MB) Zlib enabled. Server Time: 2017-10-17 16:53:44 UTC