Transformer #100023 10/05/06 12:33 PM
Joined: Apr 2002
Posts: 178
R
Reel-Break Offline OP
Member
OK I deal mostly residential but on a 3 phase xfmer 600v to 220/120 15kva Can someone bring back to basics. I have approx 39.3 amps on each phase correct?

2017 / 2014 NEC & Related Books and Study Guides
Re: Transformer #100024 10/05/06 01:03 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
FLA on a 15 kva at 208 is 15/(0.208 x 1.73)= 41.6 amps.

Re: Transformer #100025 10/05/06 01:53 PM
Joined: Apr 2002
Posts: 178
R
Reel-Break Offline OP
Member
Thanks Bob after further review it actually was 208/120 secondary.Thanks again.41.6 it is.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
Popular Topics(Views)
266,134 Are you busy
200,979 Re: Forum
189,670 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3