Reneo- I don't know if I understand your statment.
Quote
As I read it, you can use the "10 ft" tap rules only within the same panel or gear. Your light would not qualify.
You can tap a feeder and exit the taped area via a raceway and go 10' feet. You can't exit the second panel and continue the tap. If they are Service conductors, there is no length limitation.