Okay- I understand how you have interperted this text. Your stress is on "outlets installed." I too see how it could be enforced that way. But, and this is a big but, if we install an outlet and I agree with you I'm sure what an outlet is, the code requires it to be grounded 410.18 for lighting outlets and 406.3 receptacle outlets. There is a whole list of reguirements for GFCI protection for receptacles installed in location itemized in 210.8. When we get t0 210.12 they are talking about installing a circuit to feed the outlets in the bedrooms. It is clear that this circuit is required to have AFCI protection for the entire circuit. There is no wording that says "AFCI protection is required for an existing bedroom circuit." There was some talk about asking for AFCI protection on bedroom circuits when there a Service change involving the breakers feeding the bedrooms but that didn't make it into the code. So the more I think about the issue I can accept the fact that adding an outlet to an existing circuit will not necessarily trigger changing to AFCI protection of the existing circuit. Adding a circuit on the other hand does require AFCI protection.

[This message has been edited by George Little (edited 03-12-2005).]


George Little