Very unlikely a ground will open a 15 amp breaker from a 120 volt source unless there is already a good load on it.

The combined resistance resistance of the rod at the service and whatever electrodes are connected to the power company source would have to be less than 8 ohms. If you got down to 6 ohms it would take some time to trip, to get a 'fast' trip IMO you will need to get down to 2 or 3 ohms.

IMO you would need some unusual conditions to have less than 8 ohms total. [Linked Image]