I do not think that there is anyway to connect the neutral to earth in a way that can limit the difference of potential by very much for 120 volt faults.

Take a ground rod and bang it into the earth, now connect a conductor to it from a 15 amp 120 volt source.

Will it trip the breaker?

If you where barefoot would you touch this ground rod?

As I understand it we connect the neutral to earth for two reasons. Lightning and a power company fault that sends high voltage toward your home.

How about this, we have the plumbers always use plastic water and gas lines. For a grounding electrode we drive rods or use Ufers.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts