It can be anywhere from the load end of the drop to the disconnect enclosure.

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.


Greg Fretwell