Just a few thoughts:
1) The European receptacles are rated 10A, 13A or 16A. Does the NEC allow any of these ratings on a 15A breaker?
2) If it turns out that the NEC requires a 20A breaker for the 16A receptacle, you need to check with the manufacturer that the receptacle is listed for this use.
3) The British 13A receptacle is not ideal for use on 120-120V systems, unless there is a GFCI. (There is a fuse in the plug which should be on the line side.) All other connectors should work fine from a technical point of view.
UL has a European branch, which is responsible for approving the Danish connectors but they also approve the German plugs. Check with them if they have given any European receptacles a UL listing for the US. I doubt it, but who knows?